Hi, I have recently carried out a PIR on a church. The equipotential bonding to the gas and water go back to the sub main in a meeting room where the stop tap and meter are. What code should be assigned as these should go back to the origin?
 
Re: PIR codes

Hi, I have recently carried out a PIR on a church. The equipotential bonding to the gas and water go back to the sub main in a meeting room where the stop tap and meter are. What code should be assigned as these should go back to the origin?

Not neccessarily.

You now need to do the calcs to ascertain wether or not the earthing conductor of the distribution circuit is large enough to do the job of CPC and MPBC.

If it is, the water & gas bonding conductors are connected to what is technically known as a BEMT (Building Earth Marshalling Terminal). There is nothing wrong with this arrangement providing the earthing conductor above is large enough to function as both above.
 
  • Like
Reactions: 1 person
Re: PIR codes

Do a continuity test from the bond back to the MET, if you get <=0.05 ohms I would code 4 it, otherwise I would code 2 it
 
  • Like
Reactions: 1 person
Code 4 the lack of labeling!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
PIR on a Church.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
asbarker,
Last reply from
netblindpaul,
Replies
5
Views
1,565

Advert