chrish_1977

Hi everyone in advance, carried out a PIR today, nothing special 8 circuits on a dual rcd board, supply is TN-S. Done a Ze at service head and got 0.10 ohms (very good i thought). However here is my problem, the radial for the boiler and the ring circuits came out at 0.90 approximately. R1+R2 are 0.23 approximately and length of run is about 15-20 metres.

It has a crabtree starbreaker board ( with the enclosed busbar) has anyone else had high readings when testing or is it just me.

Checked all screws for tightness and were all ok, even checked all sockets. Couldn't find anything obvious

Thanks in advance

Chris
 
a bit of an effect caused by the MCBs, esp if you are using the no-trip loop test. as long as the readings are below the permitted max. ( which at 0.9 ohms is , for a 32A type b and all lesser rated MCBs). job's sound.
 
Have you measured the impedance of the mcb
 
alternatively you could derive Zs from Zs= Ze+ ( R1+R2 ). your continuity readings look spot on. (a 10m radial in 2.5/1.5 should give around 0.2ohms.)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
PIR today
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
chrish_1977,
Last reply from
telectrix,
Replies
3
Views
1,707

Advert