Hi hope someone can help. The shed in the garden is about 15m away from the house. Its supply is spurred from kitchen ring via a 30Ma RCD/13A FCU, the load side of the FCU (2.5mm flex) runs outside and underground (within metal conduit) to an adaptable box where its joined to 2.5mm SWA which runs to the shed. At the shed the SWA is terminated into a 13A FCU, which supplys' 2 sockets and 2 strip lights.


Does this installation require a TT earth system as a matter of course. As it is now the earthing arrangement is via the CPC (including SWA). The house has TN-S system.

Thanks
 
Hi hope someone can help. The shed in the garden is about 15m away from the house. Its supply is spurred from kitchen ring via a 30Ma RCD/13A FCU, the load side of the FCU (2.5mm flex) runs outside and underground (within metal conduit) to an adaptable box where its joined to 2.5mm SWA which runs to the shed. At the shed the SWA is terminated into a 13A FCU, which supplys' 2 sockets and 2 strip lights.


Does this installation require a TT earth system as a matter of course. As it is now the earthing arrangement is via the CPC (including SWA). The house has TN-S system.

Thanks

can i ask why didnt you run the swa from the outside point by the fcu to the shed, seems an odd way to run power to your shed ?????????
 
To update, ive found that exporting the TN-S is not looked at favourably; so does the SWA need to be earthed via the TT.
 
Last edited:
No the SWA dont start at the house FCU, it starts at an adaptable box under the patio. Dont know why I didn't install it, but i see what you mean

if it was me i would be looking into getting it change (you might not like that) because unless he has applied some gel and maintenance free connectors, water could get in and corrode / short thing out bad practice if you ask me
 
To update, ive found that exporting the TN-S is not looked at favourably; so does the SWA need to be earthed via the TT.

I think if you managed to export TNS anyone looking at it would be very impressed! How on earth you can sell an earthing system to another country is beyond me!

However if you were talking about extending an existing TNS earthing system and equipotential zone to include an outbuilding then there is no problem at all so long as you do it properly with respect to the requirements for bonding.
If there are extraneous conductive parts in the shed then there would have to be a main bond of the appropriate size for the intake position (normally 10 mm for a domestic supply)

If you did need to create a TT earth for the shed then the SWA would not be connected to this, it would need to be isolated from the TT earth and connected to the TNS. The bonding and cpcs in the shed would connect back to the MET of the TT system.
 
Its concreted in
you have just found a nice little job as all joints must be accessible so you might as well rip it out and run in armoured cable into the house,or possibly install a weatherproof isolator then you will not need to rip whole of existing cable out. Simply run new armoured cable from supply side of isolator into property.
 
No im not the customer, its a friends house and he wants me to check it out visually. I told him it looks OK, but was not sure about the earthing (although from what i gather here the tn-s earth is OK to use).

The crack is he wants a new CU and all the certificates for his house and dont want any surprises about the shed when he gets around to finding someone to do the job. I told him I cant do it immediately because I dont have a meter, and maybe he would be better off getting someone part P. Im just checking it for any obvious f ups which could be re mediated before-hand. From the sound of it its just the inaccessible armoured connection (is that a regulation that all joints have to be accessible, or is just a matter of good practice) ?

Cheers
 
So you're not an electrician then?

He's better off getting someone fully qualified and ignoring all claims about 'being par p'
Especially considering that part p has nothing to do with carrying out a condition report.
 
Whats it matter if im a diyer or not, im not doing the job, im trying to learn something

"No im not the customer, its a friends house and he wants me to check it out visually. I told him it looks OK, but was not sure about the earthing (although from what i gather here the tn-s earth is OK to use).

The crack is he wants a new CU and all the certificates for his house and dont want any surprises about the shed when he gets around to finding someone to do the job. I told him I cant do it immediately because I dont have a meter, and maybe he would be better off getting someone part P. Im just checking it for any obvious f ups which could be re mediated before-hand. From the sound of it its just the inaccessible armoured connection (is that a regulation that all joints have to be accessible, or is just a matter of good practice) ?

Cheers"

you shouldnt be looking at it at all not even for advice if your not in the know
 
Thanks, have to have a word about this one. Customer wont like having patio dug up thou.:biggrin:

No im not the customer, its a friends house and he wants me to check it out visually. I told him it looks OK, but was not sure about the earthing (although from what i gather here the tn-s earth is OK to use).

The crack is he wants a new CU and all the certificates for his house and dont want any surprises about the shed when he gets around to finding someone to do the job. I told him I cant do it immediately because I dont have a meter, and maybe he would be better off getting someone part P. Im just checking it for any obvious f ups which could be re mediated before-hand. From the sound of it its just the inaccessible armoured connection (is that a regulation that all joints have to be accessible, or is just a matter of good practice) ?

Cheers

Whats it matter if im a diyer or not, im not doing the job, im trying to learn something

Keep going........

Diggingahole_zps1406dd80.jpg
 
you shouldnt be looking at it at all not even for advice if your not in the know[/QUOTE]

No, why not, who are you anyways. Is there a law saying i cant look at things
 
No, why not, who are you anyways. Is there a law saying i cant look at things


More to the point, who the hell are You, to be dishing out electrical advice on a subject you clearly don't have a Scooby Doo about?? Are you one of these failed electrical trainee's that fell by the wayside or what??
 
Thanks, have to have a word about this one. Customer wont like having patio dug up thou.:biggrin:

No im not the customer, its a friends house and he wants me to check it out visually. I told him it looks OK, but was not sure about the earthing (although from what i gather here the tn-s earth is OK to use).

The crack is he wants a new CU and all the certificates for his house and dont want any surprises about the shed when he gets around to finding someone to do the job. I told him I cant do it immediately because I dont have a meter, and maybe he would be better off getting someone part P. Im just checking it for any obvious f ups which could be re mediated before-hand. From the sound of it its just the inaccessible armoured connection (is that a regulation that all joints have to be accessible, or is just a matter of good practice) ?

Cheers

i dont know anyone that call mates/friends customers, so come on lay all your cards on the table and tell the truth you installed the power/ supply to the shed and now your unsure of the earth procedure :hammer:
 
More to the point, who the hell are You, to be dishing out electrical advice on a subject you clearly don't have a Scooby Doo about?? Are you one of these failed electrical trainee's that fell by the wayside or what??

For a start pal, im not dishing out advice im asking for it; and to add that im qualified with 2360 pt's 1 & 2 and have 12 + years experience in commercial.
 
you have just found a nice little job as all joints must be accessible so you might as well rip it out and run in armoured cable into the house,or possibly install a weatherproof isolator then you will not need to rip whole of existing cable out. Simply run new armoured cable from supply side of isolator into property.

Out of interest do you rip out and redo all hidden joints you come across? Daz
 
Yeah im just double checking, Ive always worked for others who have sorted that side of it. Just keeping myself interested mate.

Good lad!!

It's very dangerous stuff this electricery if you don't know what you're doing with it so it's better to safe than sorry.

They're all good lads on here who will all do their best to keep you safe & sound and it's not true what you may have heard about Our Tony ... he's not really a grumpy old git - it's just a little act he puts on and he's as good as gold really.. :)
 
Good lad!!

It's very dangerous stuff this electricery if you don't know what you're doing with it so it's better to safe than sorry.

They're all good lads on here who will all do their best to keep you safe & sound and it's not true what you may have heard about Our Tony ... he's not really a grumpy old git - it's just a little act he puts on and he's as good as gold really.. :)

Great, its a good resource this website !
 

Reply to Power to outside shed, does it need TT earthing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, just a quick one on an earthing arrangement for a radial circuit on a wooden workshop I have just had installed. I have run a 3 core 2.5mm...
Replies
7
Views
267
Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
575

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock