Hi hope someone can help. The shed in the garden is about 15m away from the house. Its supply is spurred from kitchen ring via a 30Ma RCD/13A FCU, the load side of the FCU (2.5mm flex) runs outside and underground (within metal conduit) to an adaptable box where its joined to 2.5mm SWA which runs to the shed. At the shed the SWA is terminated into a 13A FCU, which supplys' 2 sockets and 2 strip lights.


Does this installation require a TT earth system as a matter of course. As it is now the earthing arrangement is via the CPC (including SWA). The house has TN-S system.

Thanks
 
Hi hope someone can help. The shed in the garden is about 15m away from the house. Its supply is spurred from kitchen ring via a 30Ma RCD/13A FCU, the load side of the FCU (2.5mm flex) runs outside and underground (within metal conduit) to an adaptable box where its joined to 2.5mm SWA which runs to the shed. At the shed the SWA is terminated into a 13A FCU, which supplys' 2 sockets and 2 strip lights.


Does this installation require a TT earth system as a matter of course. As it is now the earthing arrangement is via the CPC (including SWA). The house has TN-S system.

Thanks

can i ask why didnt you run the swa from the outside point by the fcu to the shed, seems an odd way to run power to your shed ?????????
 
To update, ive found that exporting the TN-S is not looked at favourably; so does the SWA need to be earthed via the TT.
 
Last edited:
No the SWA dont start at the house FCU, it starts at an adaptable box under the patio. Dont know why I didn't install it, but i see what you mean

if it was me i would be looking into getting it change (you might not like that) because unless he has applied some gel and maintenance free connectors, water could get in and corrode / short thing out bad practice if you ask me
 
To update, ive found that exporting the TN-S is not looked at favourably; so does the SWA need to be earthed via the TT.

I think if you managed to export TNS anyone looking at it would be very impressed! How on earth you can sell an earthing system to another country is beyond me!

However if you were talking about extending an existing TNS earthing system and equipotential zone to include an outbuilding then there is no problem at all so long as you do it properly with respect to the requirements for bonding.
If there are extraneous conductive parts in the shed then there would have to be a main bond of the appropriate size for the intake position (normally 10 mm for a domestic supply)

If you did need to create a TT earth for the shed then the SWA would not be connected to this, it would need to be isolated from the TT earth and connected to the TNS. The bonding and cpcs in the shed would connect back to the MET of the TT system.
 
Its concreted in
you have just found a nice little job as all joints must be accessible so you might as well rip it out and run in armoured cable into the house,or possibly install a weatherproof isolator then you will not need to rip whole of existing cable out. Simply run new armoured cable from supply side of isolator into property.
 

Reply to Power to outside shed, does it need TT earthing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
543
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock