ukpablo

I know there has been alot of threads regarding this, but could anybody give me a few pointers to what checks, what order u do before removing the old cu..............or whilst doing a quote?!

Ie after removing cu cover!

:)

thanks
 
I know there has been alot of threads regarding this, but could anybody give me a few pointers to what checks, what order u do before removing the old cu..............or whilst doing a quote?!

Ie after removing cu cover!

:)

thanks
When going round to price to give me more of an idea i do an insulation test on whole board, check bonding and earthing arrangements and do a ze test, i then tell the customer if i find any problems whilst the board is being changed they will be told of a cost before i proceed, its stood me well so far
 
do u do it at 250v? ask to disconnect all eqpt on ccts? test all neutrals , disconnected one at a time to the neutral bar to confirm no borrowed neutrals?
 
if you check at 250v(l+n) joined with appliances connected -you won't know if a low reading is equipment or fixed wiring though

borrowed neutrals-you won't know by testing between circuits at board -unless lamp(or load)
that borrows a neutral is switched on
 
Yeah at 250v, connect L and N together and test between that and earth, not a great test but does give you some idea if there is an insulation fault, a few people say to do a pir but how many people want to pay for that as they're only after a quote, and they probably want numerous quotes off different contractors to check prices, its only to give me an idea on the state of the wiring and as long as i explain first that there may be other problems whilst the new cu is being installed they're fine about it, never had a problem yet but i am quite charming:D
 
I always check bonding, Ze, class 2 fittings present in bathroom.

And then always explain to customer and also fully state on the quote,

...that after the board change should any underlying faults become present these will need to be located and rectified at £xx/hour + materials
 

Reply to Pre checks before changing CU in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
Hi all I'm after some advice on 2 way CU in a garden office which is 'buzzing' when I turn on or increase the tempreture of the wall mounted...
Replies
6
Views
577
I removed my baseboard electrical heaters (1981 installed) due to finishing off the room. When I had a new AC ductwork installed they changed the...
Replies
2
Views
403
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
422

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock