Hi. Testing an old lighting circuit today after a c/u change. First few readings were all fine. Then on one rose I got a reading of 0.5 ohms switch closed (fine) and 186 ohms switch open.

Is this indicative of an insulation problem or something else? I did an IR test and got 0.75 ohms but it was a bit rushed and couldn't be sure it wasn't just an error. That is very low surely? I'll do that again tomorrow.

I'd be grateful for suggestions!
 
Thanks. A fitting wouldn't give a continuity reading both ways though would it? I need to be sure of the ir test first I guess. Also it's rcd protected (tested fine) and that's not tripping.
 
Hi. Testing an old lighting circuit today after a c/u change. First few readings were all fine. Then on one rose I got a reading of 0.5 ohms switch closed (fine) and 186 ohms switch open.

Is this indicative of an insulation problem or something else? I did an IR test and got 0.75 ohms but it was a bit rushed and couldn't be sure it wasn't just an error. That is very low surely? I'll do that again tomorrow.

I'd be grateful for suggestions!
IR Test 0.75 ohms are you sure you have that right, it's always best practice to do the testing prior to any CU changes
 
It's just a lighting circuit so no neon and disconnected the smoke alarm. I did rush it so just closed all light switches and tested ir between line and cpc. IR could well be an erroneous reading but the continuity reading I repeated again and again.
 
It's just a lighting circuit so no neon and disconnected the smoke alarm. I did rush it so just closed all light switches and tested ir between line and cpc. IR could well be an erroneous reading but the continuity reading I repeated again and again.
Sure you're right. It's my c/u and the old tiny wylex board was packed full and the frame was falling apart from woodworm! Decided to just change it and pick up the peices afterwards.
 
If Neutral and earth are connected in the CU bars and the main switch is closed then when the light switch is open the meter could measure a resistance loop, via the supply neutral earth connection, through the load and this could give a high reading of the sort of level you have measured.
 
i assume the 0.75 ohms IR is a typo and you meant Mohms?
 
  • Like
Reactions: David M
Did you leave the lamps in?
 
Ze @ board was 0.2. R1R2 was 0.5. Didn't directly test as didn't want to energise it.

The ir must have been an error and I'll look in to it more tomorrow. Was 0.7 ohms nor m ohms! Most likely I'm just testing a lamp or something although as I say would ir line to cpc pick up this?

The continuity issue I'm sure about (that's what made me jump to ir test) so I'll dig further tomorrow. Just wondered if anyone magiclly had a solution from their experience!
 
if you has an IR reading of 0.7 ohms, that would equate to 343A. surely that would cause a hell of a bang.
 
Exactly! It's been running fine prior to my c/u change. I'm sure the continuity reading is right and pretty sure my ir reading is wrong which leaves me confused! Looks like I'll be doing some head scratching and floor boars lifting tomorrow (after I do a very well considered ir test).
 
Just a thought - I know some of the the loft light switches we install on new builds have a neon light on the switch.

Michael
 
What cable?, pvc , that is a very low reading, lamps out.?Maybe something else on the circuit.TV booster etc.
 
Am I the only one who has no idea what these readings are all about.
 
  • Like
Reactions: SparkyChick
No damp areas? Almost like there is something else in the circuit? Or when you IR'd did you have cpc on the bar still with neutral connected?
 
could there be a switch with built in ilumination ?

1374576861-36217500.jpg
 
I'm not brave enough,to ask what the readings were,before the board swap...;)
Get the impression that there wasn't any testing before CU change hope I'm wrong
 
It always mystifies me when an (alleged) low IR is encountered that a neon always seems to get the blame. This would only happen on a L-N test, the OP has not specified what IR test has been carried out but I doubt it's L-N. Or is it OP?
 
  • Like
Reactions: David M
Tested polarity of incoming supply, ze@ board, direct zs and pfc of several points on system and bonding before hand. All were fine. The board was a mess and a real tangle of too short cables.

I freely admit to being new to this so as an aside is it really common practice to do a full set of tests on every part of every circuit before a board change?

In this instance it's my board and any problems that arise need to be fixed by me anyway. Surely safer and easier once a new board in place.
 
No damp areas? Almost like there is something else in the circuit? Or when you IR'd did you have cpc on the bar still with neutral connected?
Thanks anthony. This is helpful. I did indeed have the cpc still connected to the bar. Hadn't realised this could introduce problems. I'll update this post at the end of the day with the results! Hopefully just that and an incorrect ir test...
 
  • Like
Reactions: Anthony_wayne
Yes it's always best to IR test before CU change why? because you are adding RCDs to the system, and any IR N-E L-E will trip the RCD, nothing more frustrating than changing CU all nice and neat, then do your testing, no bonding IR faults file:///C:/Users/Pete/Downloads/Best-Practice-Guide-1-Issue-3-(1).pdf
 
Yeah can see the logic. Point taken. IR tests are such a pain though!
Even worse pain is not IR testing and the RCDs trip and you have to start ripping your nice neat CU to bits to find the fault
 
You still need to clarify which conductors you IR tested between to get the 0.7Mohms (assuming this is what you meant). If you do thorough tests then you can start to eliminate the possibilities causing the fault (again assuming there is one). Its good practice to be methodical with your testing rather than just rushing and second guessing.
 
Thanks everyone. Lesson learnt. My error on both.

The cpc continuity is now fine. I'd left cpc in cu met bar. When I removed it the readings were fine.

again, my error with ir. Reading was as stated by others actually 0.7 m ohms. Looks like I've got an issue with the lighting insulation.

Methodical step by step testing the correct way I completely agree, but hadn't realised leaving cpc in met caused errors which lead me down the wrong path. Thanks.
 
It's less the leaving the CPC in the main earth bar and more to do with the neutral conductor being left connected. The correct prescribed method is to leave the cpc connected, but remove both line conductors.
 
Thanks everyone. Lesson learnt. My error on both.

The cpc continuity is now fine. I'd left cpc in cu met bar. When I removed it the readings were fine.

again, my error with ir. Reading was as stated by others actually 0.7 m ohms. Looks like I've got an issue with the lighting insulation.

Methodical step by step testing the correct way I completely agree, but hadn't realised leaving cpc in met caused errors which lead me down the wrong path. Thanks.
I understand that you are relatively new to the industry (you mentioned this earlier in the thread) Inspection & testing isn't just about taking readings and checking them against what is accepted. Its also about understanding what the tests are for, why the readings are what they are and the implications of such, whether acceptable or not.
Fault finding requires understanding and knowledge of testing, also experience which has to be earned.
I have watched many a spark just go through the motions without any thought to why he/she is doing the tests in the first place.
That's why in my opinion methodical thorough testing and a clear understanding of what you are doing and looking for is vital.
Its great that you are questioning your readings, but its important that those readings are accurate, appropriate and correctly interpreted.
 
It's less the leaving the CPC in the main earth bar and more to do with the neutral conductor being left connected. The correct prescribed method is to leave the cpc connected, but remove both live conductors.
It should be clear that this is the action to take for IR testing and that continuity testing should normally be undertaken with no possibility of parallel paths reducing the reading.
 
It should be clear that this is the action to take for IR testing and that continuity testing should normally be undertaken with no possibility of parallel paths reducing the reading.

Agreed mate, though we were talking about his IR test so thought that was clear enough. I see a lot of experienced sparkies still disconnecting the CPC for the IR tests, they don't believe it changed until you show them GN3.
 
So this had nothing to do with R1+R2 then:confounded:
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert