Domestic house, ring final circuit on an rcbo, end to end tests: r1 = 0.95 ohms, rn = 0.98 ohms, r2 = 1.02 ohms.
It's rare a reading is too suspiciously good!
Sane R1+R2 of around 0.52 for most of house except kitchen area where readings increase wildly suggesting several spurs off spurs so will be looking into this.
IR tests L+N -> E at 500v was fine.
So far I've only seen ordinary T+E on this circuit, no metal conduit / trunking etc.
I'm slightly struggling to come up with reason for disproportionately low r2 when compared with r1 and rn.
There is no continuity between cpc for either leg of this circuit and the earth bar, all other circuits connected.
I did wonder if r2 is in fact correct and r1 and rn are high due to poor connections, tomorrows job is pulling it apart.
I'm struggling to imagine a bridge in the circuit that is only bridging the cpc.
Any other ideas folks?