R1+R2 continuity both ways

Discuss R1+R2 continuity both ways in the UK Electrical Forum area at ElectriciansForums.net

S

shinypen

Hi. Testing an old lighting circuit today after a c/u change. First few readings were all fine. Then on one rose I got a reading of 0.5 ohms switch closed (fine) and 186 ohms switch open.

Is this indicative of an insulation problem or something else? I did an IR test and got 0.75 ohms but it was a bit rushed and couldn't be sure it wasn't just an error. That is very low surely? I'll do that again tomorrow.

I'd be grateful for suggestions!
 
Thanks. A fitting wouldn't give a continuity reading both ways though would it? I need to be sure of the ir test first I guess. Also it's rcd protected (tested fine) and that's not tripping.
 
Hi. Testing an old lighting circuit today after a c/u change. First few readings were all fine. Then on one rose I got a reading of 0.5 ohms switch closed (fine) and 186 ohms switch open.

Is this indicative of an insulation problem or something else? I did an IR test and got 0.75 ohms but it was a bit rushed and couldn't be sure it wasn't just an error. That is very low surely? I'll do that again tomorrow.

I'd be grateful for suggestions!
IR Test 0.75 ohms are you sure you have that right, it's always best practice to do the testing prior to any CU changes
 
It's just a lighting circuit so no neon and disconnected the smoke alarm. I did rush it so just closed all light switches and tested ir between line and cpc. IR could well be an erroneous reading but the continuity reading I repeated again and again.
 
It's just a lighting circuit so no neon and disconnected the smoke alarm. I did rush it so just closed all light switches and tested ir between line and cpc. IR could well be an erroneous reading but the continuity reading I repeated again and again.
Sure you're right. It's my c/u and the old tiny wylex board was packed full and the frame was falling apart from woodworm! Decided to just change it and pick up the peices afterwards.
 
If Neutral and earth are connected in the CU bars and the main switch is closed then when the light switch is open the meter could measure a resistance loop, via the supply neutral earth connection, through the load and this could give a high reading of the sort of level you have measured.
 
Ze @ board was 0.2. R1R2 was 0.5. Didn't directly test as didn't want to energise it.

The ir must have been an error and I'll look in to it more tomorrow. Was 0.7 ohms nor m ohms! Most likely I'm just testing a lamp or something although as I say would ir line to cpc pick up this?

The continuity issue I'm sure about (that's what made me jump to ir test) so I'll dig further tomorrow. Just wondered if anyone magiclly had a solution from their experience!
 
Exactly! It's been running fine prior to my c/u change. I'm sure the continuity reading is right and pretty sure my ir reading is wrong which leaves me confused! Looks like I'll be doing some head scratching and floor boars lifting tomorrow (after I do a very well considered ir test).
 
could there be a switch with built in ilumination ?

1374576861-36217500.jpg
 
It always mystifies me when an (alleged) low IR is encountered that a neon always seems to get the blame. This would only happen on a L-N test, the OP has not specified what IR test has been carried out but I doubt it's L-N. Or is it OP?
 
Tested polarity of incoming supply, ze@ board, direct zs and pfc of several points on system and bonding before hand. All were fine. The board was a mess and a real tangle of too short cables.

I freely admit to being new to this so as an aside is it really common practice to do a full set of tests on every part of every circuit before a board change?

In this instance it's my board and any problems that arise need to be fixed by me anyway. Surely safer and easier once a new board in place.
 
No damp areas? Almost like there is something else in the circuit? Or when you IR'd did you have cpc on the bar still with neutral connected?
Thanks anthony. This is helpful. I did indeed have the cpc still connected to the bar. Hadn't realised this could introduce problems. I'll update this post at the end of the day with the results! Hopefully just that and an incorrect ir test...
 
Yes it's always best to IR test before CU change why? because you are adding RCDs to the system, and any IR N-E L-E will trip the RCD, nothing more frustrating than changing CU all nice and neat, then do your testing, no bonding IR faults file:///C:/Users/Pete/Downloads/Best-Practice-Guide-1-Issue-3-(1).pdf
 

Reply to R1+R2 continuity both ways in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock