Okay, if i had a radial circuit wired in 6mm/6mm swa and the measured R1/R2 was 0.16ohms. What table or resistance value would you personally use to calculate the length of that circuit as a reference point, and what length would you calculate?

Since you disagree with using the onsite tables and the procert one, im curious what you would use?
I think we have ended up slightly at cross purposes. I have no issue with anyone using OSG, BS7671, Pro Certs, or any other reliable reference of the resistance of copper in order to work out expected R1+R2 values.

My emphasis was intended to be on the "all the OP needs".
I'm a little bit concerned that anyone is having to undertake EICRs and asking some of the questions above, apparently without being provided with the latest regs book or OSG.
I don't mind using this forum to further my own understanding and in turn to try and help other people increase their understanding, but sometimes it feels like people are put in impossible situations by their employers and are expected to run before they can walk.
 
Two things concern me about this thread:
1. The OP is conducting EICRs but not doing any live testing.
2. The OP is conducting EICRs without knowing basic things like how to calculate R1 and R2 values.
3. Sorry there is no third thing
 
Two things concern me about this thread:
1. The OP is conducting EICRs but not doing any live testing.
2. The OP is conducting EICRs without knowing basic things like how to calculate R1 and R2 values.
3. Sorry there is no third thing

The third thing for me is that the OP doesn't seem to see the problem of the first two points.
 
I have a good understanding on electrics and testing and what I should be looking for and testing
The company I now work for only require us to do dead testing and then calculate the zs readings
All I was wondering is if they was a table about I could use as a guide for r1 r2 readings so I know my readings are correct or slightly high and I need to do abit of further investigation on circuits
Previously I’d do dead and live testing and I’d be able to check check the r1 r2 results by the zs readings
 
If I had my own way I’d be doing dead and live testing but when the company doesn’t want us doing it and to just calculate zs results then I’m going to do what I’ve been told to
Two things concern me about this thread:
1. The OP is conducting EICRs but not doing any live testing.
2. The OP is conducting EICRs without knowing basic things like how to calculate R1 and R2 values.
3. Sorry there is no third thing
 
Does nobody do any live testing?
Who signs the certs?
 
All I was wondering is if they was a table about I could use as a guide for r1 r2 readings so I know my readings are correct or slightly high and I need to do abit of further investigation on circuits
For EICR purposes, the two things that come to mind are how close the calculated Zs is to the limit for the device, and a sense of how big the property you are in is and whether a reading seems plausible. The more you do the easier that gets.
e.g. if you're re in 2 up 2 down and you get 1.5 ohms for an immersion heater circuit then a bit of head scratching is due.

The other thing you can do is try RN+R2 or use a wander lead to obtain a 2nd frame of reference, and whether it's R1, R2 or both that have a loose connection.

I'm assuming that you are allowed to do Ze, Zs@DB and RCD tests, and your company only prohibits live Zs readings?
 
This is a 'modern' take on Zs testing that you don't do it live except for socket outlets where there is no risk of exposed live parts but as @timhoward asks do you carry out Ze and rcd tests.
 

Reply to R1 + R2 expected readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
744
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
973
hi all just got a Q regarding how to find R1 then second Q how to find R2 what i did so far was mutiplying each answer for1.67 so I could get the...
Replies
11
Views
903

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock