Hi All,

Busy doing an EICR and on 2 of the Socket Rings for the dead test I get the following results:
Step 1: End to End (0.32 ohm r1, N ) & (r2 = 0.51 ohm)
Step 2: r1 to N 35.6 ohm
Step 3: r1 to r2 no reading

At first I thought maybe I was testing the wrong r2 in/out but I traced the cable back and it matched the T&E so it's definitely matched & crossed correctly.
Also before I isolate the board I always check the sockets with my Kewtech "socket & see" device, which is normally pretty accurate, and this didn't flag any issues!

Any ideas on why there is no r1 + r2 reading and why r1 + N is off the charts?
 
Do you get similar readings from multiple socket outlets? If that's a specific socket, you might be seeing the effect of high-resistance contacts e.g. from corrosion.The end-end test is OK because only the continuity of cable via the terminals is involved, and the Socket-&-See indicates correctly because its very low current requirement will enable it to 'See' through many kilohms of resistance (which is why they are not a great idea) and show a connection even when it is off the scale of the continuity range of the MFT.
 
Do you get similar readings from multiple socket outlets? If that's a specific socket, you might be seeing the effect of high-resistance contacts e.g. from corrosion.The end-end test is OK because only the continuity of cable via the terminals is involved, and the Socket-&-See indicates correctly because its very low current requirement will enable it to 'See' through many kilohms of resistance (which is why they are not a great idea) and show a connection even when it is off the scale of the continuity range of the MFT.
It's a fairly new installation, less than a year! The whole circuit shows the same readings at each socket, and when opening up all of the conductors are seated fine which is why i'm puzzled.
The socket & see helps me decide my sample size, and to be fair has found reverse polarity / broken earth on a few occasions, but I still check polarity with the MFT at all the sockets!
[automerge]1593791046[/automerge]
Are you sure the cables aren’t crossed over MCBs if your getting the same end to end readings on 2 circuits?
Cables are matched and not crossed over MCB's, double checked all of them making sure that the conductors came from the same T&E sheathing from both in/out cables and then cross connected!
 
Take the socket and see out if the equation, test direct to the socket terminals with your mft see if you get the same result.
 
start with a wander lead. measure R1 from CU to sockets. repeat for R2.
 
test R! at each socket. from the readings you'll get an idea of how they are run. when you get to an open circuit, that's when to investigate. could even be something screwed on wall piercing the L. kitchen fitters are notorious for this.
 

Reply to r1 + r2 No Reading, Open Circuit! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
601
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock