Discuss Rcd not tripping in the UK Electrical Forum area at ElectriciansForums.net
Doctorsparks
I'm stumped, fitted new cu in one bed house today RCD would not trip using test button or on test. The only time it trips is when a load is put onto socket circuit, or the socket on the cooker isolator, no faults have been found during testing.
Its a TNC-S system ze of 0.16ohms IR of >999 on all circuits, zs good on all circuits.
i thought it may have been a defective RCD so I replaced it but no join? I have tested both RCD's on my board when I got home both worked!
Any ideas?
Are you certain the RCD was connected correctly...polarity?,load and mains sides correct?
Also test the RCD with the tester directly on the load terminals with nothing else connected.
Sounds like a neutral on the wrong bar.
I have occasionally tested an RCD at the L-N output, wondered why it would not trip and then given myself a good kicking for being so stupid. The test button always worked though.
If the RCD won't work with anything connected something simple is wrong, there were some RCDs that needed a few meters of cable atttached or they would not work, cannot remember the make though. Have you tried testing from the accessory? Not GN3 method but would give you more ideas. The test button should always work though.
Failing that contact the manufacturer.
Good luck.
if it worked when you tested it at home, then go back and re-fit (supply only) . check you have correct voltage l-n supply side, switch on and check load side then test. remember, it works by measuring imbalance.
Might be worth double-checking the IR for evidence of N-E faults on any finals, not just the ones that cause tripping. A hard N-E short downstream of the RCD can prevent the test button working as well as failing tests with the MFT.
It's more of an annex. It's got cooker, one ring and two lighting circuits, it's just been renovated none of the wiring has been changed I'm just upgrading the board and earthing.
Thanks for for all the advice am there now going to disconnect everything re test and reconnect.
It's an excel?
Reply to Rcd not tripping in the UK Electrical Forum area at ElectriciansForums.net
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...