I have to run a 70mm SWA sub circuit over a distance of 70metres in a 4in duct under ground. The cable will run from the main incoming electricity boards supply (busbar after meter). I know I will need an isolator at the front but do I need an RCD also, like a 100mA time delay???
Current being drawn will be around 120A max. The install is on a farm and the supply is a 200A CT monitored single phase TNS supply.
If anyone can point me in the right direction regarding the correct chapter in the regs it would help, if its the case I need the RCD!!
 
I believe the requirements for RCD protection in Agricultural/Horticultural premises are:
30mA for circuits supplying socket-outlets (32A and below), 100mA for circuits supplying socket-outlets above 32A and 300mA for all other circuits.
Obviously this is dependant upon Zs being low enough for the RCDs to operate.
 
The SWA cable buried in ducts at the correct depth as laid out in the regs would not need RCD protection , how ever circuits from the consumer unit it supplies will depending on the installation methods and useage check out section 705 page 216 of the regs , you will need a switch fuse however to protect the cable so as not rely on the supply fuses
 
Last edited by a moderator:
705.411.1 In cicuits, whatever the type of earthing system, the following disconnection devices shall be provided:
(i) In final circuits supplying socket-outlets with rated current not exceeding 32A, an RCD having the characteristics specified in Regulation 415.1.1
(ii) In final circuits supplying socket-outlets with a rated current more than 32A, an RCD with a rated residual operating current not exceeding 100mA
(iii) In all other circuits, RCDs with a rated residual operating current not exceeding 300mA.
 

Reply to RCD or NOT??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
899
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
699

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock