Test L/N linked at 500v.
NO! Test both L-E and N-E...….just avoid L-N.so am I correct in thinking that I should only test the n&e wires and at 250 volts
NO! Test both L-E and N-E...….just avoid L-N.so am I correct in thinking that I should only test the n&e wires and at 250 volts
If you are just fault finding then I would stick at 250v with loads connected. There is nothing to be gained in this scenario from using 500v IR. You will pick it up on 250v. I know if you link L&N it there is then 0v pd between them but the 250v is a safety net if L or N is opened for any reason in circuit with a termination, switching or MCB etc and you then risk 500v across vulnerable equipment.Test L/N linked at 500v.
There's no need to link L-N to IR test to earth for fault finding. The linked L-N method of IR testing is for initial verification of a new/altered circuit, or periodic testing. Fault finding does not follow standard test procedures as required for the above, if you link L-N you will not know whether the fault is L-E or N-E
The OP. Have just noticed he has asked two separate questions ... Both have the same answer though lolWho is He?
Sorry I have confused you with the OP.The OP. Have just noticed he has asked two separate questions ... Both have the same answer though lol
Yes. He meant test between L&E and then N&E as seperate tests as opposed to L linked to N & tested to E.if n&e are joined and then tested to earth surely this this would not be poss surely I would need to test the n and e unjoined to get a resistance?