I'm having a problem with the CU rcd tripping out, I have installed a feed outside to my daughters hot tub using 6mm cable about 14mts in length going to a metal clad dis board and from there via a 32A mcb to a 32A switched socket, insulation is good, no damp, but when I connected up the tub the rcd tripped, I removed the connections and connected a socket to connect a kettle as a test load everytime the kettle was turned on the rcd tripped, Ideas please tia
 
Is it a single 30mA RCD for the whole house?

A bit more detail would help. It might be just the leakage of the tub is accumulating too much for the RCD. Do you have a clamp ammeter (that can measure down to mA) you could check the leakage with by clamping both tails?
 
It could be a fault in the hot tub, given it holds out on a kettle. Can you IR test the tub at 250V (just in case electronically switched) to check that L+N to E is showing tens of Mohm?

Another possibility is a N-E short somewhere (not necessarily on the new circuit). If you are on a TN-C-S supply the origin N-E voltage is practically zero so typically that only shows up if you have loads of tens of amps or more. It might be the kettle at ~10A is not enough to cause enough N-E current to divert, but the tub coming on pump and heaters at 30A (or more, if motor surge is simultaneous, etc) is enough to reach threshold.
 
If you suspect a N-E short then switch off the main supply (so both L & N isolated at the origin) and do a global IR taking L+N to E, maybe at some convenient socket (having made sure RCD reset and socket switched on!).

Again 250V is safer to play with, but L+N to E should always be safe to test at 500V (unlike L-N on low power electronics where 250V is max to try just in case).
 
It could be a fault in the hot tub, given it holds out on a kettle. Can you IR test the tub at 250V (just in case electronically switched) to check that L+N to E is showing tens of Mohm?

Another possibility is a N-E short somewhere (not necessarily on the new circuit). If you are on a TN-C-S supply the origin N-E voltage is practically zero so typically that only shows up if you have loads of tens of amps or more. It might be the kettle at ~10A is not enough to cause enough N-E current to divert, but the tub coming on pump and heaters at 30A (or more, if motor surge is simultaneous, etc) is enough to reach threshold.
It trips on the kettle as well and that is 3kW
 
could it be a N-E fault on a completely different circuit, so that when a large load is applied on the new circuit, the RCD sees imbalance . had it before where a N-E fault in a shower switch tripped the RCD that fed the other half of a dual RCD board. time for an electrician methinks.
 

Reply to Rcd tripping on new hot tub circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
575
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
998
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
789
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock