I was called out yesterday to a house to have a look at a wall mounted heater in a bedroom that had stopped working. Had a quick look, and noticed that the heater was controlled by a 20A DP switch. No FCU. In the CU, it was on a 32A MCB. Upon further investigation, I found that there were two 3kw heaters on this circuit. Basically, the 10mm^2 shower circuit had been repurposed to supply these heaters. Nothing unusual about that but the way it was done was a bit rough (in my view). The 10mm^2 cable was terminated into a cooker outlet plate, then 2 x 2.5mm^2 cables came out of this plate, immediately into 2 x unswitched FCUs, then onto the heaters which had local 20A DP switches. I fixed her problem by simply replacing a fuse. But it got me thinking how I would have done this job and if the current situation is acceptable. The connections in the cooker outlet were sound, no cable can be overloaded, so at the time I couldn't immediately fault it. I suppose the cooker outlet wasn't designed for the purpose it is being used for. If I were doing this I would probably just stick a small 2 way CU with 2x 16A MCBs in it on the end of the 10mm^2, or find a more suitable way of joining the cables.
Any thoughts?
 
The 2 x 16A MCBs would cover it. But I guess the question is - is it necessary? The 2.5 should be able to meet fault disconnection for 32A MCB ok (?) so it's overload current that remains. This was covered by the 13A FCUs used, but from immersions I've found many of these don't like 3kW loads. Does reg 433.3.1 (ii) help us? The heater draws 12.5A and it's hard to see (to me anyway :) ) how one could draw a current that would overload the 2.5 ?
 
they are fixed loads, so over current protection is not required. only short circuit protection is needed.
 
If the OP had fitted a small CU, where would it be located?

I am not fitting anything, just thinking about how the job was done. It could go where the 2 x FCUs are now, in a cupboard off the landing. Obviously the CU idea is totally unnecessary anyway!
 

Reply to Reused shower cable (for heaters) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
160
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
269
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
800
Done a few EICR's recently and having a blonde moment regarding storage heaters. All storage heaters in the property are rated at 1.5kw and fed...
Replies
9
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock