Farmelectrics

-
Arms
Reaction score
520
Just done some small alterations to a training room it's a 4mm radial in dado trunking that was already there there is 7 pcs to be plugged into circuit I suggested making it into a ring but the engineer were working for says its ok I thought all pcs had to be on ring du to high integratity earthing
 
BS7671 in there somewhere, you're correct but I don't think they have to be on a ring, 2 cpc's though (ringed as they say) one of which can be conduit
 
Ok Kas so if I or should I say we run a 4mm earth back to db connected in separate earths of course this would solve the issue just for the record though what spark would disconnect an earth of a live circuit any way and be on the end of the earh leakage from the pcs always baffled me this one
 
Computers can generate leakage currents that can cause RCD tripping problems as they can also have functional earthing requirements that suppress noise on the computer supply.
If the leakage current is high, say with ten or more computers, then the cpc should be doubled and, for a radial run, in a ring, but the live conductors do not need to be in a ring, it is only to ensure that the cpc connection is not broken by accident (i.e. high integrity earthing).
The cpcs should also be terminate in the accessories separately.
 
Last edited:
I didn't write the regs lol, personally I'd of put them on a ring, I've worked on contracts where they've specced 4mm rings as standard so I'd of gone with your suggestion for the sake of a bit a cable and you would of then achieved the high integrity earthing as well, but I can see no reg where computers have to be on a ring, it could be a radial with 2 cpc's with one being a conduit or trunking.
 
all you need to do is use both earth tags on each socket, then from the last socket on the radial, take a 4.0mm single g/y back to DB. terminate in a different hole.
 
Will do tel but if you didn't what problems could this cause and how would you ever come into contact with this earth leakage as you wouldn't disconnect the earths at the db nosing the circuit was live your thoughts please
 
no problems with a radial only, the ringing of the cpc is belt and braces in case of a cpc snapping off at a terminal. you can measure the earth leakage with a clamp meter if you need to, a pc has a typical leakage of around 3mA.
 
It is not coming into contact with the earth leakage that is the main problem, although that is the effect we are trying to control, it is ensuring that the piece of equipment is continuously connected to the MET.
Because the suppression filters, SM power supplies, etc., generate a potential on the earth that can deliver over 10mA there is a risk of harm to someone touching any exposed conductive parts of the equipment if the equipment is not earthed, I know a lot of the desk IT kit is double insulated now, but there is a still a reasonable amount that is not and more in server rooms.
Also the lack of an earth will render the suppression useless as the leakage current is from a functional earth and without it the transients have nowhere to go.
 
It is not coming into contact with the earth leakage that is the main problem, although that is the effect we are trying to control, it is ensuring that the piece of equipment is continuously connected to the MET.
Because the suppression filters, SM power supplies, etc., generate a potential on the earth that can deliver over 10mA there is a risk of harm to someone touching any exposed conductive parts of the equipment if the equipment is not earthed, I know a lot of the desk IT kit is double insulated now, but there is a still a reasonable amount that is not and more in server rooms.
Also the lack of an earth will render the suppression useless as the leakage current is from a functional earth and without it the transients have nowhere to go.
its effectively an earth screen....dumping stray...
 
Personally i wouldn't have more than 5 PC workstations on any one circuit!! Having RCD protection on PC/IT work station circuits, is just asking to loose any unsaved data, but it still seems all too common to do so!! lol!!

High integrity earthing is specified for a purpose, and something that the OP's Engineer should have been aware of, and suggested a dual/ringing of the CPC
 
It's not been mentioned here, but I'm almost sure from memory that the 4mm cpc has to follow the same route as the circuit cable and to be clipped with it.
 

Reply to Ring or radial in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
681
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
430
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock