Hi all, I am rewiring my house and have a twin 30ma RCD consumer unit in the house, and a single RCD 30ma unit in the garage. The garage unit is fed via 6mm cable from a 40amp breaker in the main unit. When testing the garage unit rcd, that garage rcd and house rcd both tripped because there is no discrimination between the two. I would like to replace one of the house rcds with an S type rcd to prevent tripping in the house CU if a fault occurs in the garage circuits.
However, if I do does this mean that the rest of the house circuits protected by that rcd no longer comply with regulations as presumably the rcd protecting them will not disconnect within 200ms in the event of a 30ma fault?
If that is the case, then what is the best way around this problem? Thanks in anticipation for your help.
However, if I do does this mean that the rest of the house circuits protected by that rcd no longer comply with regulations as presumably the rcd protecting them will not disconnect within 200ms in the event of a 30ma fault?
If that is the case, then what is the best way around this problem? Thanks in anticipation for your help.