I have been asked to upgrade a fuse board, however, when I did an initial visual inspection, I noticed the main earth from the DNO is unsheathed (TN-S), it’s strands that are clearly ancient!
I haven’t yet carried out any tests. Should I get the DNO to change the earth? Will they actually bother changing it? A new smart meter has recently been fitted and the tails were upgraded - should they not have replaced the earth then?
This picture shows the MET - the other cable is main bonding.
Any thoughts?E20B2D41-8D2D-4374-8AAE-1BB43C09305A.jpeg
 
Aico 3000
Scolmore Electrical Products
This official sponsor may provide discounts for members
buzzlightyear

buzzlightyear

-
Esteemed
Arms
Cosidering it the main earth from the dno which is nowt do with you .
And all test are good for Ze then i would get some green and yellow. Tape on the main earths to show any body cuting it off and a sign earths connection do not remove .
Post automatically merged:

You also said a smarta## meter has been fitted is their a islolator near the main cut out ,other wise the tooth fairy needs to pull the main cut out .
 
Last edited:
S

Snailspark

-
  • Thread Starter Thread Starter
  • #3
Cosidering it the main earth from the dno which is nowt do with you .
And all test are good for Ze then i would get some green and yellow. Tape on the main earths to show any body cuting it off and a sign earths connection do not remove .
Post automatically merged:

You also said a smarta## meter has been fitted is their a islolator near the main cut out ,other wise the tooth fairy needs to pull the main cut out .
There has been an isolator fitted yes so no need to touch their stuff...
 
Lucien Nunes

Lucien Nunes

-
Mentor
Esteemed
Arms
This is perfectly normal, it's a bare cable soldered to the service cable lead when that was installed. The CSA is usually smaller than you would choose today but in practice invariably meets (and well exceeds) the minimum required to satisfy the adiabatic, in which case it's fine. The leccy doesn't care whether it's green & yellow. In some countries bare main earths are standard practice today, they cannot be mistaken for anything else and any damage is easily visible.
 
B

braineebird

-
I have been asked to upgrade a fuse board, however, when I did an initial visual inspection, I noticed the main earth from the DNO is unsheathed (TN-S), it’s strands that are clearly ancient!
I haven’t yet carried out any tests. Should I get the DNO to change the earth? Will they actually bother changing it? A new smart meter has recently been fitted and the tails were upgraded - should they not have replaced the earth then?
This picture shows the MET - the other cable is main bonding.
Any thoughts?View attachment 52157
Do a quick ze test. If it's a good earth I'd sleeve it and use it. If not then get the dno involved
 
telectrix

telectrix

-
Mentor
Esteemed
Arms
send your apprentice to stores for some green/yellow striped paint.
 
davesparks

davesparks

-
Mentor
Esteemed
Arms
Calculate the size of earthing conductor required and check the size against that.

Don't just go by the Ze, you could have a good Ze on an undersized conductor.
 
Midwest

Midwest

-
Esteemed
Arms
I must be the only one, that thinks that’s a mess. I’d contact the DNO and ask them to have a butchers, for flips sack!
 
C

Cid

-
If the Ze is good then dno won't be interested at all and neither should you.
 
D

Deleted member 105166

You could ferrule the two multiwire terminations at the MET (526.9.1), I imagine you'd need to use the uninsulated variety to get sufficient length so as to maintain two terminal screws per termination, as an insulated ferrule would be too short and restricted by its insulation.
 
telectrix

telectrix

-
Mentor
Esteemed
Arms
You could ferrule the two multiwire terminations at the MET (526.9.1), I imagine you'd need to use the uninsulated variety to get sufficient length so as to maintain two terminal screws per termination, as an insulated ferrule would be too short and restricted by its insulation.
similar thoughts. could just be tidied up a bit. no need for ferrules though as it's 7 strand, just give it a bit of a twist.
 
S

Snailspark

-
  • Thread Starter Thread Starter
  • #12
This is perfectly normal, it's a bare cable soldered to the service cable lead when that was installed. The CSA is usually smaller than you would choose today but in practice invariably meets (and well exceeds) the minimum required to satisfy the adiabatic, in which case it's fine. The leccy doesn't care whether it's green & yellow. In some countries bare main earths are standard practice today, they cannot be mistaken for anything else and any damage is easily visible.
If it all checks out ok - I will change the earth from the MET to my new fuse board to a proper one anyway..
 