I have been asked to upgrade a fuse board, however, when I did an initial visual inspection, I noticed the main earth from the DNO is unsheathed (TN-S), it’s strands that are clearly ancient!
I haven’t yet carried out any tests. Should I get the DNO to change the earth? Will they actually bother changing it? A new smart meter has recently been fitted and the tails were upgraded - should they not have replaced the earth then?
This picture shows the MET - the other cable is main bonding.
Any thoughts?E20B2D41-8D2D-4374-8AAE-1BB43C09305A.jpeg
 
Advertisement - Content continues below

buzzlightyear

-
Arms
Esteemed
Cosidering it the main earth from the dno which is nowt do with you .
And all test are good for Ze then i would get some green and yellow. Tape on the main earths to show any body cuting it off and a sign earths connection do not remove .
Post automatically merged:

You also said a smarta## meter has been fitted is their a islolator near the main cut out ,other wise the tooth fairy needs to pull the main cut out .
 
Last edited:
  • Thread Starter Thread Starter
  • #3
Cosidering it the main earth from the dno which is nowt do with you .
And all test are good for Ze then i would get some green and yellow. Tape on the main earths to show any body cuting it off and a sign earths connection do not remove .
Post automatically merged:

You also said a smarta## meter has been fitted is their a islolator near the main cut out ,other wise the tooth fairy needs to pull the main cut out .
There has been an isolator fitted yes so no need to touch their stuff...
 

Lucien Nunes

-
Mentor
Arms
Esteemed
This is perfectly normal, it's a bare cable soldered to the service cable lead when that was installed. The CSA is usually smaller than you would choose today but in practice invariably meets (and well exceeds) the minimum required to satisfy the adiabatic, in which case it's fine. The leccy doesn't care whether it's green & yellow. In some countries bare main earths are standard practice today, they cannot be mistaken for anything else and any damage is easily visible.
 
I have been asked to upgrade a fuse board, however, when I did an initial visual inspection, I noticed the main earth from the DNO is unsheathed (TN-S), it’s strands that are clearly ancient!
I haven’t yet carried out any tests. Should I get the DNO to change the earth? Will they actually bother changing it? A new smart meter has recently been fitted and the tails were upgraded - should they not have replaced the earth then?
This picture shows the MET - the other cable is main bonding.
Any thoughts?View attachment 52157
Do a quick ze test. If it's a good earth I'd sleeve it and use it. If not then get the dno involved
 

telectrix

-
Mentor
Arms
Esteemed
send your apprentice to stores for some green/yellow striped paint.
 

davesparks

-
Mentor
Arms
Esteemed
Calculate the size of earthing conductor required and check the size against that.

Don't just go by the Ze, you could have a good Ze on an undersized conductor.
 

Midwest

-
Arms
Esteemed
I must be the only one, that thinks that’s a mess. I’d contact the DNO and ask them to have a butchers, for flips sack!
 
D

Deleted member 105166

You could ferrule the two multiwire terminations at the MET (526.9.1), I imagine you'd need to use the uninsulated variety to get sufficient length so as to maintain two terminal screws per termination, as an insulated ferrule would be too short and restricted by its insulation.
 

telectrix

-
Mentor
Arms
Esteemed
You could ferrule the two multiwire terminations at the MET (526.9.1), I imagine you'd need to use the uninsulated variety to get sufficient length so as to maintain two terminal screws per termination, as an insulated ferrule would be too short and restricted by its insulation.
similar thoughts. could just be tidied up a bit. no need for ferrules though as it's 7 strand, just give it a bit of a twist.
 
  • Thread Starter Thread Starter
  • #12
This is perfectly normal, it's a bare cable soldered to the service cable lead when that was installed. The CSA is usually smaller than you would choose today but in practice invariably meets (and well exceeds) the minimum required to satisfy the adiabatic, in which case it's fine. The leccy doesn't care whether it's green & yellow. In some countries bare main earths are standard practice today, they cannot be mistaken for anything else and any damage is easily visible.
If it all checks out ok - I will change the earth from the MET to my new fuse board to a proper one anyway..
 

telectrix

-
Mentor
Arms
Esteemed
If it all checks out ok - I will change the earth from the MET to my new fuse board to a proper one anyway..
good move. the DNO provided earth will outlast me and probably you as well. sometimes the old school solutions are best. ( now where's my wind-up Megger?).
 
The service cable needs terminating, there should be a cover over the cable end at the bottom of the cut out. In effect the cable is single insulated. DNO would upgrade main earth at same time.
 

davesparks

-
Mentor
Arms
Esteemed
The service cable needs terminating, there should be a cover over the cable end at the bottom of the cut out. In effect the cable is single insulated. DNO would upgrade main earth at same time.
The service cable is terminated and appears to have a heat shrink breakout boot fitted so the cable is in effect not single insulated.
 
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Should I get the main earth changed by the DNO? in the Electrical Forum area at ElectriciansForums.net

uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom