Discuss single wired armour in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

snowplough

Hi Guys,

Just wondrerd if you could give me any ideas or where to look , trying to answer an old 2391 test question,

Q. What 5 things would you inspect on s.w.a fastened to cable tray,but it asks spec in regards to the cable and not construction of the tray.

Iappreciate your help

Locket
 
Cables of correct current carrying capacity; security and spacing of fastenings on vertical and horizontal - max distance will be different vertical compared to horizontal. spacing between cable if more than one could interfere with CCC and correct segregation of band 1 and 11 circuits if applicable; Any internal bending radii correct; correct for ambient temps. Any joints and connections mechanically good and accessible for inspection.

Don't be put off by the tray just think for any cables

edit : btw the S in SWA stands for steel :)
 
Last edited by a moderator:
Many Thanks Push rod,

Does segregation of band 1 and 11 only apply to trunking or can it apply to cables on tray as well?

My lecturer once told me at college, no matter what any one says S.W.A stands for Single W.... A not Steel W.... A........

What do you think


Many Thanks

Locket
 
Many Thanks Push rod,

Does segregation of band 1 and 11 only apply to trunking or can it apply to cables on tray as well?

There needs to be a physical partition between them on tray reg 528.1 (iv)
There is also aBS standard about it i think.

My lecturer once told me at college, no matter what any one says S.W.A stands for Single W.... A not Steel W.... A........

What do you think

I'm no expert but Brian Scadden (author of loads of books) is, and he abbreviates steel wired armour to swa so i'll go with him

Many Thanks

Locket

Cheers Locket - just hit the "thanks" button now and again ;)

edit : oops just saw you did - :eek: .
 
Last edited by a moderator:
Actually, there doesn't have to be a physical partition.
Segregation can be achieved if the ELV cable insulation is rated at or above the LV rating.


Quite correct. Not experienced in recognising band I circuits being run in band II/low voltage cables mind - would they be immediately noticeable or would you just assume they were band II in the first place - if you know what i mean.
 
If there is nothing on the cable stating it's rating, I will assume it's not appropriately rated.
SWA for instance is generally rated to 1000V, and industrial Beldon type (twisted pair, cat 5 etc.), is 300V.
Whereas burgular alarm/phone cable generally has nothing on it.
Obviously when being installed the cable rating should be known, prior to installation and appropriate measures taken.
 
Last edited by a moderator:
on jobs ive been on,weve hadto run armoured 5 pair and 1 pair, and they still want segregation. Asfar as im concerned, the cable is insulated for highest coltage present, and its protected by SWA, if there ever was a problem.
 
Hi wire puller ,
you have got a point,

Changing subject,
Can you tell me, when you have a high Zs value and you your measured value is higher after rule of thumb ,

3 ways to get Zs down
Am i right in thinking you can change protective device for one that gives a smaller Zs

Shortening the length of the circuit, making just R1 shorter or R1+R2?

Making the csa bigger, is that the csa of R1 ,or the csa of R1 +R2

Hope you can help, im revising for 2391 on thurs.

Many thanks

Locket
 
Hi wire puller ,
you have got a point,

Changing subject,
Can you tell me, when you have a high Zs value and you your measured value is higher after rule of thumb ,

3 ways to get Zs down
Am i right in thinking you can change protective device for one that gives a smaller Zs


I think you mean a PD that allows a larger Zs eg changing a c type mcb to a b type
Shortening the length of the circuit, making just R1 shorter or R1+R2?

Making the csa bigger, is that the csa of R1 ,or the csa of R1 +R2

Hope you can help, im revising for 2391 on thurs.

Many thanks

Locket

Often doing the actual calculation instead of using the rule of thumb allows more leeway.

Shortening the circuit length will affect R1+R2. Incidentally upgrading (if needed) the meter tails and the main earth can also lower measured Zs .

Increasing the CSA of either line or cpc, mostly likely both, if you are increasing cable size, will reduce resistance and so reduce Zs.
 
Many Thanks Pushrod,

Iincidently when you say decreasing circuit length will effect R1+R2, I take it you meant it will also lower Zs ,

Many Thanks

Locket
 
Many Thanks Pushrod,

Iincidently when you say decreasing circuit length will effect R1+R2, I take it you meant it will also lower Zs ,

Many Thanks

Locket
 

Reply to single wired armour in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys, I don’t really know where to post this, sorry if it’s in the wrong place. After posting a thread about old lead sheathed cable in my...
Replies
22
Views
2K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K
Good Morning All I would like to give a really big thanks to this forum and especially to Marconi who has over the past weeks and months been a...
Replies
0
Views
687

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock