Hi
Currently on a job at a hospital where we are installing temporary site supplies to canteen toilet block and office.
The supply is Tncs from hospital but the hospital electrician and contractor doesn’t want us to install earth rods in case of services below ground and they’re not prepared to scan ground.
Hospital electrician says we can use PME supply as long as it’s on RCD but surely this isn’t correct as if a broken PEN conductor will make all cabins live potentially and rcd won’t pick this up?
Also what other option do we have if can’t use pme and they don’t want TT. Surely under regs it has to be TT and there’s no arguing?

Thanks
 
They will be fine on TN-C-S.
 
You could alway fit a Matt e or similar pen fault device
 
potentially and rcd won’t pick this up?
Also what other option do we have if can’t use pme and they don’t want TT. Surely under regs it has to be TT and there’s no arguing?
I agree with the site spark, banging a earth rod in a ground would you take responsibility for it with all the pipe work around the hospital.
 
Are you sure it's TNCS? I'd have thought that's unusual for a hospital, they normally have pretty big supplies if not 11kV incoming which would all be TNS.

But either way it will have earth rods for the backup generatir, a lightning protection system and other bonded metalwork buried in the ground. All this will add up to quite a nice earth electrode to keep things safe if a PEN fault occurs.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Lincoln

Thread Information

Title
Site Temps earthing question
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Alan Marriott,
Last reply from
davesparks,
Replies
4
Views
1,594

Advert