I have an installation that I maintain and the DNO have recently changed their pole transformer. Since this change I have been unable to do earth loop tests. The supply comes from a HV to LV transformer and there is a HV earth rod right next to the neutral/earth rod for the HV to LV transformer.

The installation is a TT system with one earth rod. For some reason I get 186V L-E and 66V N-E and 252V L-N at the cut out fuse when the fuse and the neutral are removed.

Could it be stray voltage from the HV system?
And why would this not give me an earth loop reading on my tester?

Thanks in advance
 
It's not giving you a EFLI as Uo is 186v as is below testers parameters.

If you are really getting those readings at the origin if supply then phone DNO asap

** edit ** Dave beat me to it!
 
  • Like
Reactions: Baddegg
I have an installation that I maintain and the DNO have recently changed their pole transformer. Since this change I have been unable to do earth loop tests. The supply comes from a HV to LV transformer and there is a HV earth rod right next to the neutral/earth rod for the HV to LV transformer.

The installation is a TT system with one earth rod. For some reason I get 186V L-E and 66V N-E and 252V L-N at the cut out fuse when the fuse and the neutral are removed.

Could it be stray voltage from the HV system?
And why would this not give me an earth loop reading on my tester?

Thanks in advance
What HV system are you referring to SJE?
 
The installation is a TT system with one earth rod. For some reason I get 186V L-E and 66V N-E and 252V L-N at the cut out fuse when the fuse and the neutral are removed.

Are you sure it's TT and not PNB (TNCS), is this the only installation fed from this pole mount transformer?
The reason I ask is that if you are disconnecting things from the DNO's cutout, which you are obviously not allowed to do, you could have caused this dangerous condition if it is PNB.
 
Are you sure it's TT and not PNB (TNCS), is this the only installation fed from this pole mount transformer?
The reason I ask is that if you are disconnecting things from the DNO's cutout, which you are obviously not allowed to do, you could have caused this dangerous condition if it is PNB.

I have had the DNO out to investigate and they removed the cut out and neutral for me. Also, yes we are the only connection to the transformer.
 
I have had the DNO out to investigate and they removed the cut out and neutral for me. Also, yes we are the only connection to the transformer.

Did they confirm that it is TT? It seems quite unusual for a single service from a pole mount transformer l.
 
I can confirm it is definitely TT, the DNO say they have tested their supply and it is good... so really don't know.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Stray voltage in Neutral - help
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
SJE392,
Last reply from
SJE392,
Replies
10
Views
2,405

Advert