Hi All,
Think I know the answer but just looking for other options....I have been asked to install sub main 60 amp isolation switch supplying already installed 16mm T & E under floor to RCD protected consumer unit. Approx. 2 mtr of 16mm is in wall. I understand that regs require RCD protection for cable in wall, but I am trying to avoid loosing all circuits in event of trip. Would this also apply for meter tails from cut out passing through/up walls? Any ideas?
 
Yes it would.
I've got around a problem with meter tails once by having a 3mm metal plate fabricated to cover meter tails which were enclosed for a 1M run in a kitchen which used to be a garage.
 
or you could protect the buried section with earthed metallic protection.
 
Hi jimmy jazz
Regs state that rcd protection is for cables buried less than 50mm in the wall and use of unskilled persons. I would possibly install a 100mA rcd fo your main switch, so so your 30mA rcd protecting a bank of circiuts or 30 mA rcbo will trip first avoiding the whole board losing power in the event of a fault on 1 circuit.
 
Hi jimmy jazz
Regs state that rcd protection is for cables buried less than 50mm in the wall and use of unskilled persons. I would possibly install a 100mA rcd fo your main switch, so so your 30mA rcd protecting a bank of circiuts or 30 mA rcbo will trip first avoiding the whole board losing power in the event of a fault on 1 circuit.

but the buried cable needs protecting by a 30mA RCD unless mechanically protected.
 
have a word with dno about changing to PME. get hold of them using the emergency number on lecky bill(even not emergency just go through options) and their normally quite happy to come out, check and upgrade to PME at no charge usually even if head needs changing. might give you some better options for seperating circuits from one rcd, then with right mech protection in wall cable won't need rcd protection.
 

Reply to Sub main RCD protection in the Australia area at ElectriciansForums.net

Similar Threads

Replacing DB’s with all singing all dancing RCBO’s Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor...
Replies
11
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
553

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock