Search the forum,
Discuss Supplementary bonding in the UK Electrical Forum area at ElectriciansForums.net
Pretty sure the supply water pipe will be copper, but the plumber hasn't put it in yet
You'll probably find he'll use plastic out of sight and copper for show with lots of push fits more good measure. You just have to IR test to see if it's extraneous or not.
But was it not the case that the cpc's of any circuits entering the special location should be bonded, under the 16th edition ammendment?
You are correct in that if the 17th edition criteria are not met, protective conductors of all power and lighting points within zones must be bonded to all ECP's. GN8 does, however, state that cpc's may be used as bonding conductors. Therefore, provided that all ECP's were bonded together either in, or close to the bathroom, and are subsequently bonded to at least one cpc (connected to all the others), then continuity will be guaranteed.
Old cylinder cupboard with all pipes bonded together then connected to the CPC of the immersion.
And wasn't it only equipment that was class 1 needed supp bonding anyhow?
Reply to Supplementary bonding in the UK Electrical Forum area at ElectriciansForums.net
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...