and if the supply voltage drops within permissible limits, e.g. @peak times, that's a drop of 6% which makes a mockery of your 3%.
Think the OP has already binned that ideaNobody has mentioned the reference method. Clipped direct has a higher ambient temperature than buried, which is usually lower as it's cooler below 500cm. So, go for the one which has the higher impact on the temperature of the cable, so at least choosing clipped direct was right. And I still don't know why you are thinking about running 10mm armoured in conduit. The steel armour inside is there to protect the conductors. Good luck getting armoured around a bend
I'll try to keep up!!!Think the OP has already binned that idea
Next time you get lines or detention.I'll try to keep up!!!
I've just calculated this and it IS 10mm, it can't be longer than your previous measurement and be a smaller conductor!!. If your friend says it's overkill, I hope can be at the enquiry with you to explain the fireAlso I say this as I got a reply from someone else saying 10mm SWA is "over kill"