Discuss Tape light receiver/driver help in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi

I’m going to add some strip lighting (tape lights) into a walk in wardrobe and hopefully this should be straight forward and I’d like to do this task myself, I already have a socket in the area but no switches so I’ve bought a Quinetic receiver and wireless switch and a Ansell driver and tape lights

I can change the socket to fused spur but this is where my questions begin

The quinetic receiver is 6 amp so is that the fuse that I need in the fused spur and what thickness of cable would I need between the fused spur and receiver? It will be around 20cm from the fused spur

Also is there a minimum distance between the receiver and driver or can they sit side by side
The Quinetic part number is QUR303
The Ansell driver part number is AD75W

Any help greatly appreciated
 
In almost every case a 3A fuse is your choice.

Exceptions are things taking more than 750W or with very big switch-on surges. The 6A it talks about includes the load, that is a lot of lighting! The driver you mention is going to take well under 1A but might blow a 1A fuse due to surges, so 3A would be a sane choice and an easy fuse to source (you can get 1,2,3,5,7,10 and 13A but many are not easy to find).

These days lighting should be on a RCD protected supply, do you know if your sockets are protected? A look in your CU = counsumer unit = fusebox should show any RCD, it will have a test button and ought to mention 30mA as its sensitivity.
[automerge]1588535674[/automerge]
For the cable you can use anything from 0.5mm and larger with a 3A fuse, but you might find 0.75mm cable easier to work with.

If you need two outlets (to keep a single socket and add a FCU beside it) you can use a twin back box such as these:
https://www.NoLinkingToThis/c/elect...#category=cat7230011&numberofgangs=1___1_gang

But they are wider than a double so wall needs cutting out, and no going back! Of course you can put two single sockets in if you really did need to go back.
 
Last edited by a moderator:
For your response @pc1966

The consumer unit was fit earlier this year and is British General CFSWP110 100A Mains Switch, 10 x RCBOs (3 x 6A, 2 x 16A, 4 x 32A & 1 x 40A) if that helps
I have some 3 amp fuses and 0.75 cable so that’s good

Is the receiver and driver ok side by side

Thanks
 
That is great to hear, an all-RCBO setup is definitely your best choice!

So you can use any FCU for feeding it and cable/fuses are just fine.
 

Reply to Tape light receiver/driver help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am installing some driveway lights. The customer wants to be able to switch them on from t he house, but also have a PIR at the driveway...
Replies
12
Views
633
Hi All, I am looking to install a Quinetic double gang in line receiver switch (QURS2W) in my hallway on the ground floor to control the lights...
Replies
4
Views
1K
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
662
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi, I have recently moved house and what to replace the garden shed. The shed has some electrics; a double socket with a fused light switch and a...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock