Hi

Could someone please tell me the correct way to do insulation resistance test on a ring circuit, i have have been shown a couple of different ways and want to make sure i am doing this correctly.

Thanks Paul
 
Hi,
The way I normally do it is both the line conductors clipped together, both neutrals and both cpc's.

500v on tester and you want a reading of over >2M ohms.

hope this helps,
Sav
 
Hi again,
I was a bit vague with my description, but do it as acat says (with the lines clipped together, neutrals together and cpc's)

Thanks acat,
Sav
 
Hi again,
I was a bit vague with my description, but do it as acat says (with the lines clipped together, neutrals together and cpc's)

Call me strange, but I don't see the point of clipping the cables for a ring...

Ring continuity should be checked before insulation resistance, so is there a method to this madness?
 
Call me strange, but I don't see the point of clipping the cables for a ring...

Ring continuity should be checked before insulation resistance, so is there a method to this madness?

How would do an insulation resistance for a ring final circuit then ??

Thanks and regards,
Sav
 
I agree no need to clip them together as you are doing an IR test it does not serve a purpose. I would however clip linve and neutral together on one clip and earth on the other and do this test first. That way anything that may have been left on the circuit or neons wont effect the reading nor will any damage be done.


Chris
 
I agree no need to clip them together as you are doing an IR test it does not serve a purpose. I would however clip linve and neutral together on one clip and earth on the other and do this test first. That way anything that may have been left on the circuit or neons wont effect the reading nor will any damage be done.


Chris
That maybe so for a periodic, but for initial verification on a new installation ??
 
After you've finished with your continuity tests, before you reconnect any cables, choose one end of the ring (make sure none of the wires on the other end are touching) and do your IR tests the same as you would for a radial.

SIMPLES:D
 
Last edited by a moderator:
so am i right saying that you connect the phase from one leg and neutral from the other leg then test on the other end of phase and netural then repeat for phase to earth and neutral to earth.

thanks for responses
 
That maybe so for a periodic, but for initial verification on a new installation ??

Its suitable for both so I am told and was given 612.3.3 of BRB I do however agree on inital verification nothing should be plugged in but you may still have neons to contend with.


Chris
 
I must admit i do clip them together just in case i get zapped by the return legs , how i do it is live to earth neutral to earth and live to neutral , but first do the test on 250 volts just in case something is plugged in , if i get a suspect reading i double check for any plugged in items once im sure i then retest at 500 volts , its a longer process but cheaper than having to replace a washing machine or worse thats taking into account that the continuity test is ok
 
Last edited by a moderator:
I must admit i do clip them together just in case i get zapped by the return legs , how i do it is live to earth neutral to earth and live to neutral ,but first do the test on 250 volts just in case something is plugged in , if i get a suspect reading i double check for any plugged in items once im sure i then retest at 500 volts , its a longer process but cheaper than having to replace a washing machine or worse

I take it all back that is a good reason for joining them together and I think knowing me it is bound to happen so I think I will start doing that;)


Chris
 

Reply to testing a ring in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
826
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
578
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
810
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
474

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock