Discuss Testing Help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
N
nicsin02
Hi guys starting a new job testing commercial properties, i have passed my 2391 a few years ago and im just looking to refresh myself<
1: when doing an IR test on circuits protected by rcbo's to i have to disconnect both neutral and earth flying leads?
2: what are the flying leads on rcbo's actually for
3: when carrying out a Z's on a socket ring does everything have to be unplugged from sockets
4: same as number 3: for continuity tests
Many Thanks
1, Yes disconnect everything, but the cpc's must remain connected to the main earthing terminal whilst the circuit is under test.
2, The cream one is a functional earth, it wont work without it connected, the neutral is to enable connection to the neutral bar.
3, No
4, No, but i would disconnect to ensure no faulty loads give dodgy readings.
I would get GN3 and refresh yourself, it will all come back to you in a flash.
Cheers...........Howard
I leave the neutral and earth flying leads in place and disconnect the circuit line and neutral from the RCBO. As above, leave the CPC connected to the earth bar.
3, No
On the 'functional earth' point, what do they actually do? they test perfectlt without them
Reply to Testing Help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...