Discuss tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I'm sure a lot of people do :) Is this a study question or is there another reason you want to know this.
as you're new, i'll allow a bit of latitude. obviously dead tests before energising. then break that down a bit further. you don't IR test a circuit until you've determined that the circuit is complete. i.e. continuous. so continuity, the IR, then you know it's safe to powere up. then live tests, Zs, then test |RCD.
Think about the sequence of tests and if they need to be energized and if you could do them if energized or not??? eg, r1+r2??? What would happen if you linked out Live and CPC then turn it on???
Reply to tests in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Hello fellow sparks, I’m looking to do my testing and inspection course which starts on the 30th of April, but I have not got much testing...
Hello everyone. I’m looking for an Electrical Improver job and lots of the job advertisements says I need an IPAF. None of them actually say...
Hi, I currently have a Megger 1730 v1 which is fine for all functions except the 2 wire (L-E) no trip loop test, (no 3 wire loop test on my 1730)...
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...