Yeah, I was watching the ideal international sparky championship. Aussie, Canadian, American and a Chinese fella in the final. Someone in the comments section asked where the British entry was. The comments were “Anyone who uses Rings, are not invited” and the like. These foreign morons have no idea of the concept. They probably would have trouble wiring one.

I thought you were going to say a joke; at the sparkie championship, there was an Aussie, Canadian, American & Chinese's sparks in the competition.

When asked, where were the British entries, they said they weren't invited as they would run rings around us. :)
 
Real time constraints when carrying out EICR's at acceptable cost mean ring circuits are often not properly verified and the inspector has to make judgement calls on whether the circuit is correctly wired. That said I love testing my own rings and calculating whether measured readings are spot on!
As far as radials go there was a long thread on here a while back where an OP stated rings should be outlawed because they are often abused by Kev the kitchen fitter and DIY Dave, his point was radials are much safer.
But unskilled persons being unable to correctly alter a ring is not a reason for banning it, ban Kev and Dave...not the ring!!
That point of view also ignores the potential danger of a radial. One bad or broken connection of the cpc may result in every downstream point working and apparently ok but not having an earth.
The problem with properly verifying a ring is not lost on a radial either (for the record, I think spurs off a ring are the Devil's work and should be you last resort).

Say you have a 32A radial in 4mm, how often would an EICR check it had not been extended in 2.5mm for much the same risk as a double-spur on a ring?

Yes, the usual radials on 20A might be safe for 2.5mm but it is the same underlying problem - if some idiot has extended a circuit badly it is not always apparent from the readings.

I guess checking the worst case Zs is OK for the MCB is probably good enough for most cases, but complete verification of an unknown is a costly and difficult situation in both cases.
 
The problem with properly verifying a ring is not lost on a radial either (for the record, I think spurs off a ring are the Devil's work and should be you last resort).

Say you have a 32A radial in 4mm, how often would an EICR check it had not been extended in 2.5mm for much the same risk as a double-spur on a ring?

Yes, the usual radials on 20A might be safe for 2.5mm but it is the same underlying problem - if some idiot has extended a circuit badly it is not always apparent from the readings.

I guess checking the worst case Zs is OK for the MCB is probably good enough for most cases, but complete verification of an unknown is a costly and difficult situation in both cases.
Indeed, and one of my bugbears on this forum is those who advise punters to have an EICR because it will identify any problems. No it wont necessarily.... and those of us tasked with carrying out EICR's are not helped by the creation of unrealistic expectations of what an EICR can identify.
 
I think the ring is for the more technical minded. The maths in it are great. Really it is not for amateurs so I can see why dumbing down is the way to go as with so many things today. The ring is dead (as it should be while working on it!) long live the ring! would be the correct use of that paraphrase.
 
I think the ring is for the more technical minded. The maths in it are great. Really it is not for amateurs so I can see why dumbing down is the way to go as with so many things today.
I don't quite understand that statement.

The "radial" in the general sense might often be used for all sorts of strange loads so calculating its safe parameters is a bit of a challenge at times.

The radial for a couple of 13A sockets is fairly easy but typically you would see 2-3 MCB sizes possibly used, and 1.5 (dodgy) / 2.5 / 4mm choices depending if it is one, a few, a lot of sockets (or quite long).

The RFC on the other hand, if you keep away from the Devil's spurs, is really simple for 99% or so of cases:
  • Use 2.5mm cable
  • Use a 32A B MCB
  • Loop the cable round from MCB, to every 13A socket, back to same MCB
  • Keep that length below 96m (or look closely at the OSG & check your DB Ze)
Yes, the RFC is dumb choice if you only have a couple of sockets at a remote-ish area, but for most general house wiring it is simple and effective.

I really think if either of them is difficult for someone to grasp then they ought not to be doing it though! But that applies to a lot of things in life.
 
I don't quite understand that statement.
To be honest I was being a bit provocative/sarcastic. I fully agree there is a place for each of the types of circuit. And the radial is essential in a number of cases. What I rail against is the disposal of the ring final circuit in favour of the radial taking over and dispensing with rfc altogether. I don't think people have thought this through actually. So we have a radial as the preferred household circuit. Branching and branches off of the branches, a kind of fractal growth of additions over the years. Now, it is you job to track down a fault. What would you prefer a nightmare of endless branches or a nice orderly ring with a crossover?
 
Agreed, the problem is the badly-done additions to either type of circuit, not the basic premise.

But you can't make something foolproof as fools are so damn inventive, just look over the "dodgy pictures" thread, etc!
 
  • Like
Reactions: Vortigern and DPG
Just had a look at the latest results on this poll...not voted myself, by the way.
Ring 27, Rad 5........I wonder how many of those radders have voted for rings too, as should be the case.
For the actual question, it should be 50/50, IMO.... both
On the other hand, I'll bet all the ringers use rads as well, although all the rads don't use rings. So the rads should beat the rings.

It must be getting cold, the rad's have come on and I've got to go, the phones ringing....
 
I voted for Radials as that is all the French allow, maximum of eight sockets on 1.5mm and twelve sockets on 2.5mm no calculations needed, all specialty outlets to be in 4mm or 6mm according to load, the list of specialty outlets is very long, but includes hob, oven, fridge, freezer, washing machine, tumble dryer.................well you get the idea.
 
Running a 4mm2 to supply a domestic fridge seems like a criminal waste of resources.
 
Running a 4mm2 to supply a domestic fridge seems like a criminal waste of resources.
About a thousand years ago, when I started, local authority spec in schools was a minimum of 4.0mm MICC to any socket, often we were running a radial to a single socket!
 
  • Like
Reactions: Vortigern
About a thousand years ago, when I started, local authority spec in schools was a minimum of 4.0mm MICC to any socket, often we were running a radial to a single socket!
Odd!

Mind you an issue with MICC was folk running in circuits based solely on the high rated current carrying capacity (that running at high temperatures allowed) and not considering higher voltage drop from thinner conductors, perhaps this was some attempt to avoid that issue at a contract level? Or to allow for additional capacity later?

But wastful, compared to simply implementing a correctly designed circuit.
 
  • Like
Reactions: DPG and radiohead
I voted for Radials as that is all the French allow, maximum of eight sockets on 1.5mm and twelve sockets on 2.5mm no calculations needed, all specialty outlets to be in 4mm or 6mm according to load, the list of specialty outlets is very long, but includes hob, oven, fridge, freezer, washing machine, tumble dryer.................well you get the idea.
I did not word that very well, what I should have said was "all specialty outlets to be in 2.5, 4mm or 6mm according to load, sorry about that, it was early. :mad:
[automerge]1598611238[/automerge]
I voted for Radials as that is all the French allow, maximum of eight sockets on 1.5mm and twelve sockets on 2.5mm no calculations needed, all specialty outlets to be in 4mm or 6mm according to load, the list of specialty outlets is very long, but includes hob, oven, fridge, freezer, washing machine, tumble dryer.................well you get the idea.

Thinking about it, that post disappeared this morning before I had finished composing it or checking it's content, when I left the Forum the post was not there, that's my excuse and I am sticking to it. :innocent:
 
Last edited:
  • Like
Reactions: DPG
On a similar note, is anyone else having keyboard problems on the forum. Money works fine in other apps, but whenever I use the enter or backstage key on here my keyboard disappears. Strange.
 
There's a rift in the "Space time continuum" on my desk that does that some times, it's either that or the Romulum cloaking device playing up.
 
  • Like
Reactions: DPG
There's a rift in the "Space time continuum" on my desk that does that some times, it's either that or the Romulum cloaking device playing up.
or just basic computer witchcraft.
 
  • Like
Reactions: DPG
The problem with properly verifying a ring is not lost on a radial either (for the record, I think spurs off a ring are the Devil's work and should be you last resort).

Say you have a 32A radial in 4mm, how often would an EICR check it had not been extended in 2.5mm for much the same risk as a double-spur on a ring?

Yes, the usual radials on 20A might be safe for 2.5mm but it is the same underlying problem - if some idiot has extended a circuit badly it is not always apparent from the readings.

I guess checking the worst case Zs is OK for the MCB is probably good enough for most cases, but complete verification of an unknown is a costly and difficult situation in both cases.
"spurs off a ring are the devil, s work" is a comment I would regard as "throwaway" in most cases, but your comments are much too measured and considered for me to take it lightly in your case. Do you really feel so strongly? (I agree by the way but would, nt use the same language). Or have you been swayed by John Ward who used the phrase "devil's work" in relation to ring circuits.
[automerge]1598645118[/automerge]
Indeed, and one of my bugbears on this forum is those who advise punters to have an EICR because it will identify any problems. No it wont necessarily.... and those of us tasked with carrying out EICR's are not helped by the creation of unrealistic expectations of what an EICR can identify.
Agreed. I often remind customers that when testing we do not have a "crystal ball" and that our meters are limited in what they can tell us. I maintain that the "visual test" is still the single most important o E we carry out
 
I maintain that the "visual test" is still the single most important o E we carry out
Any inspector who doesn't agree with that shouldn't be allowed anywhere near an electrical installation.......unless they're testing in braille, of course. ;)
 
  • Agree
Reactions: pc1966
"spurs off a ring are the devil, s work" is a comment I would regard as "throwaway" in most cases, but your comments are much too measured and considered for me to take it lightly in your case. Do you really feel so strongly
I can see why they are allowed, as they don't impact on the safety of a ring when done correctly.

But my bone of contention is the same as a badly modified radial circuit - you have far, far, more things that can be done badly where more than one 13A socket has been spurred off, etc. Also it degrades the elegant testability of a ring (the figure-of-8 style) as a higher R at some point might be bad connections/socket, or it could just be a run of cable on a spur.

So to me an installation with spurs is fundamentally a bad starting point (really you could not run the ring to/from that point, or maybe just a radial for that odd load?) and once folk start modifying it you get in to the test/verification nightmare.

But that is not an attribute of ring per se as if you do dumb stuff to a radial (i.e. creating a the Christmas tree circuit) you get exactly the same issues of being able to adequately confirm it is all safe.
 
Last edited:
Sometimes, with a physically long ring - e.g. because the circuit is some way from the distribution board (say in a large mansion) - I've found a spur or two can help keep the length of the ring down, and make the difference between a comfortable compliant and perhaps non-compliant circuit.

I'm also a fan of a spur at the origin on an RFC, where appropriate!
 
To be honest I was being a bit provocative/sarcastic. I fully agree there is a place for each of the types of circuit. And the radial is essential in a number of cases. What I rail against is the disposal of the ring final circuit in favour of the radial taking over and dispensing with rfc altogether. I don't think people have thought this through actually. So we have a radial as the preferred household circuit. Branching and branches off of the branches, a kind of fractal growth of additions over the years. Now, it is you job to track down a fault. What would you prefer a nightmare of endless branches or a nice orderly ring with a crossover?
Vortigern. I also think it would be wrong to dispose of the ring (though it looks to me inevitable). As you know I am not a fan, but it has its place and there is clearly a particular affinity among British sparks for it which in my view should certainly be respected.
Could I however comment on your point about radials. I have noticed this concept of radials been presented in several posts as "tree, s" with apparently ever extending "branches" resulting in "faultfinding been a nightmare". But where does this happen? This view does not conform with the situation on the ground in my experience. The radials in use here in socket circuits are very simple "loop in., loop out". No tree, s, no branches and faultfinding is a doddle.
[automerge]1598646521[/automerge]
I can see why they are allowed, as they don't impact on the safety of a ring when done correctly.

But my bone of contention is the same as a badly modified radial circuit - you have far, far, more things that can be done badly where more than one 13A socket has been spurred off, etc. Also it degrades the elegant testability of a ring (the figure-of-8 style) as a higher R at some point might be bad connections/socket, or it could just be a run of cable on a spur.

So to me an installation with spurs is fundamentally a bad starting point (really you could not run the ring to/from that point, or maybe just a radial for that odd load?) and once folk start modifying it you get in to the test/verification nightmare.

But that is not an attribute of ring per se as if you do dumb stuff to a radial (i.e. creating a the Christmas tree circuit) you get exactly the same issues of being able to adequately confirm it is all safe.
By "badly modified radial circuit" could you give some more examples of exactly what you mean?
 
But where does this happen? This view does not conform with the situation on the ground in my experience. The radials in use here in socket circuits are very simple "loop in., loop out". No tree, s, no branches and faultfinding is a doddle.

It may be that in future this becomes more of an issue as general socket radials are spurred off over time in much the same way as rings have been.

I don't imagine that spurs off spurs are often found in homes built in the last few years and it's more of an issue with older installations?
 
Sometimes, with a physically long ring - e.g. because the circuit is some way from the distribution board (say in a large mansion) - I've found a spur or two can help keep the length of the ring down, and make the difference between a comfortable compliant and perhaps non-compliant circuit.

I'm also a fan of a spur at the origin on an RFC, where appropriate!
That is fair enough, there will be many corner-cases when putting in a spur makes sense technically and economically. But for a long ring then I would say just do it in 4mm - still going to be cheaper than the equivalent radial(s)!
[automerge]1598647197[/automerge]
By "badly modified radial circuit" could you give some more examples of exactly what you mean?
Basically the idea behind a ring is the loads are evenly spread out and there is some diversity - as you use if for general purpose sockets, not large fixed loads like water heaters, cookers, etc., even if they are significantly under the 32A MCB rating.

But the danger of adding a spur is then it is extended from one to to be several sockets and then you have, at the attachment point to the ring, a large lumped load that is not part of the assumption for reasonably safe distribution of loads.

Finally once you have 3 wires in a socket (i.e. ring in/out and the spur) you have a greater chance of them not all being properly clamped and good connections.

Now no decent electrician would do that (add multiple sockets off a spur), but the idea that "adding a socket is fine" might lead to that happening by poor practitioners of the electrical art.
 
Last edited:
It may be that in future this becomes more of an issue as general socket radials are spurred off over time in much the same way as rings have been.

I don't imagine that spurs off spurs are often found in homes built in the last few years and it's more of an issue with older installations?
We don't have any issues with unfused
I think the ring is for the more technical minded. The maths in it are great. Really it is not for amateurs so I can see why dumbing down is the way to go as with so many things today. The ring is dead (as it should be while working on it!) long live the ring! would be the correct use of that paraphrase.
That is fair enough, there will be many corner-cases when putting in a spur makes sense technically and economically. But for a long ring then I would say just do it in 4mm - still going to be cheaper than the equivalent radial(s)!
[automerge]1598647197[/automerge]

Basically the idea behind a ring is the loads are evenly spread out and there is some diversity - as you use if for general purpose sockets, not large fixed loads like water heaters, cookers, etc., even if they are significantly under the 32A MCB rating.

But the danger of adding a spur is then it is extended from one to to be several sockets and then you have, at the attachment point to the ring, a large lumped load that is not part of the assumption for reasonably safe distribution of loads.

Finally once you have 3 wires in a socket (i.e. ring in/out and the spur) you have a greater chance of them not all being properly clamped and good connections.

Now no decent electrician would do that (add multiple sockets off a spur), but the idea that "adding a socket is fine" might lead to that happening by poor practitioners of the electrical art.
OK. Now I see where you are coming from. We don't experience that example of a "badly modified ring". The "danger of adding a spur" is not a danger we have. We don't use unfused spurs as you do.There is no possibility of the circuit been overloaded. There will only ever be a switched fused outlet off a radial for a fixed appliance (usually a gas or oil burner or such like). Loads over 1500 Watts should be on a separate circuit
 
It may be that in future this becomes more of an issue as general socket radials are spurred off over time in much the same way as rings have been.

I don't imagine that spurs off spurs are often found in homes built in the last few years and it's more of an issue with older installations?
You are spot on, most cases of spurs off spurs are from older installs and the new installs generally have adequate amount of socket outlets without requiring additional sockets, so the risk of the lazy spark not doing work correctly is reduced by the property already having sufficient amount of outlets.
 
I think the ring is for the more technical minded. The maths in it are great. Really it is not for amateurs so I can see why dumbing down is the way to go as with so many things today. The ring is dead (as it should be while working on it!) long live the ring! would be the correct use of that paraphrase.
Missed this "beauty" earlier..Ring is for "the more technically minded", "not for amateurs". You are spot on. I know who you had in mind when you wrote it and I am grateful you did, nt mention me by name (?)
 
  • Funny
Reactions: Vortigern
We don't use unfused spurs as you do. There is no possibility of the circuit been overloaded. There will only ever be a switched fused outlet off a radial for a fixed appliance (usually a gas or oil burner or such like). Loads over 1500 Watts should be on a separate circuit
That is a sane way of doing it.

Basically it is not a spur in the way I see it - you have a FCU on the ring and the remote load is off that (just like a 13A plug but without the plug/socket)?
 
We don't have any issues with unfused

Who is "we"?

The point I was making was in response to your comment about not finding branches off radial circuits, which result in a testing nightmare.

I get that the safety issue is removed with spurs from radials, but as general socket circuits on these islands have traditionally be run as RFCs, I think it's reasonable to make the point that an increase in the use of radial circuits could see as many messy circuits as additions/repairs are effected with the passing of time.
 
Who is "we"?

The point I was making was in response to your comment about not finding branches off radial circuits, which result in a testing nightmare.

I get that the safety issue is removed with spurs from radials, but as general socket circuits on these islands have traditionally be run as RFCs, I think it's reasonable to make the point that an increase in the use of radial circuits could see as many messy circuits as additions/repairs are effected with the passing of time.
That’s exactly the point you can install radials rather than rings but it would be no different to having a ring it still has the chance of spurring of multiple times like a ring main. Ring main all day long for me
 
That’s exactly the point you can install radials rather than rings but it would be no different to having a ring it still has the chance of spurring of multiple times like a ring main. Ring main all day long for me

I'm very much the layman in this discussion, and I'll openly admit to having once looked at RFCs as being the devil's work.

Time and information changed that position and I now see both forms of circuit as having equal merit. My previous disparaging thoughts about RFCs were due to being on the wrong end of shoddy workmanship and I now understand that circuits are not the cause of problems - poor design and workmanship cause problems, circuits themselves are generally blameless.
 
  • Like
Reactions: Vortigern
Circuits are always blameless and there seems to be an equal amount of derision for both the FRC and Radial on this thread, but all brought about by someone modifying the original circuit.
 
I'm very much the layman in this discussion, and I'll openly admit to having once looked at RFCs as being the devil's work.

Time and information changed that position and I now see both forms of circuit as having equal merit. My previous disparaging thoughts about RFCs were due to being on the wrong end of shoddy workmanship and I now understand that circuits are not the cause of problems - poor design and workmanship cause problems, circuits themselves are generally blameless.
That is my belief aswell I do agree that a radial is suitable in some scenarios but in most cases the ring main pros outweighs the radial pros
 
The ring final circuit; is the way things have been done in blighty since the forties. It has an elegance of it's own. Radial circuits are used alongside the rfc as standard also. Think lighting circuits for instance. Radials are commonly used for cookers and high draw equipment often. So rfc and radials are in common use.
I am aware in other countries radials are the standard. France, Ireland and Spain leap to mind. No doubt many others. Fine, if you like radials to the exclusion of rings, better not live in blighty as we do rfc here. How many times have you heard some one championing ring final circuits aggressively over radials? It seems it is a sport for those countries not endowed with the majestic rfc. I feel sure it is some kind of attempt to take away something that is at once foreign, and complex to those not versed in the system. A dumbing down of something that really seems peculiar to UK. The testing is more complex, as attested by those of the radial persuasion and how easy it is, even a "doddle" Personally rfc is fab when you put it in and do the tests, I get a strange warm feeling when the maths work out perfectly. Us English eh!
 
The ring final circuit; is the way things have been done in blighty since the forties. It has an elegance of it's own. Radial circuits are used alongside the rfc as standard also. Think lighting circuits for instance. Radials are commonly used for cookers and high draw equipment often. So rfc and radials are in common use.
I am aware in other countries radials are the standard. France, Ireland and Spain leap to mind. No doubt many others. Fine, if you like radials to the exclusion of rings, better not live in blighty as we do rfc here. How many times have you heard some one championing ring final circuits aggressively over radials? It seems it is a sport for those countries not endowed with the majestic rfc. I feel sure it is some kind of attempt to take away something that is at once foreign, and complex to those not versed in the system. A dumbing down of something that really seems peculiar to UK. The testing is more complex, as attested by those of the radial persuasion and how easy it is, even a "doddle" Personally rfc is fab when you put it in and do the tests, I get a strange warm feeling when the maths work out perfectly. Us English eh!
Cough! Cough! British!! I’m welsh so not just the English who like RFC! ??
 
And anyway doing Radials for sockets is a pain in the ar**. When you try to do two 4mm² into a stinky LAP socket! Or even worse when you have to try three, argghhhh! Even with 2.5mm² it can be a problem. Then when you attend a fault situation, you gingerly remove the socket with three 4mm² in and they pop out and you have to get them back in. This is why we don't pull things apart on an EICR, you could make the installation worse.
[automerge]1598652273[/automerge]

[automerge]1598652363[/automerge]
so not just the English who like RFC
Sorry I thought with all the devolvement going on it would not be good to be colonial and speak for others. However I stand corrected and united we stand then:)
 
And anyway doing Radials for sockets is a pain in the ar**. When you try to do two 4mm² into a stinky LAP socket! Or even worse when you have to try three, argghhhh! Even with 2.5mm² it can be a problem. Then when you attend a fault situation, you gingerly remove the socket with three 4mm² in and they pop out and you have to get them back in. This is why we don't pull things apart on an EICR, you could make the installation worse.
[automerge]1598652273[/automerge]

[automerge]1598652363[/automerge]

Sorry I thought with all the devolvement going on it would not be good to be colonial and speak for others. However I stand corrected and united we stand then:)
Haha good answer well I know one thing for sure that us welsh as much as we have a love/hate relationship with England we will always have each others back in time of need apart from when it comes to rugby ?
[automerge]1598652705[/automerge]
Haha good answer well I know one thing for sure that us welsh as much as we have a love/hate relationship with England we will always have each others back in time of need apart from when it comes to rugby ?
Looking forward to the autumn internationals
 
  • Agree
Reactions: Vortigern
  • Like
Reactions: nicebutdim
The Radial and FRC (why) debate will always go on whilst T&E is still being produced if at some point that ceases to be the case I think the RFC will go it's natural course.
 
The Radial and FRC (why) debate will always go on whilst T&E is still being produced if at some point that ceases to be the case I think the RFC will go it's natural course.

I'm not quite grasping your point about T&E, considering its widespread use in Ireland and the UK's widespread use of RFCs that run through conduit in singles.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Website
https://www.scolmore.com/products/deco/
What type of forum member are you?
Manufacturer / Distributor / Supplier / Inventor - etc

Thread Information

Title
The Ring is dead, long live the Radial!⚡
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
192

Advert

Thread statistics

Created
Scolmore,
Last reply from
static zap,
Replies
192
Views
22,485

Advert