Hi all, I'm new here so :flowers:
I have a small industrial unit with three phase and single phase installed. The single is obviously for lights, standard sockets, phone, computer etc and is working perfectly.
The three phase supplies a tyre changer (10A breaker) and an air compressor (20A breaker).
Friday night they both worked fine, and as always I turned off the isolators and went home. Saturday morning, I came in, turned on the air compressor isolator and instead of firing up, the motor buzzed for a few seconds and tripped its breaker. Turned on the tyre machine and tried the motor, it too just buzzed but would not move, it buzzes without tripping the breaker. All 240v stuff continues to work.
I reset the compressor breaker, same result - buzz and trip. Same time after time.
I looked into the board, all the 3 incoming tails measure 240v each. Across L1-L2 its 425v, across L2-L3 its 425v, across L1-L3 its 0v. Does this make sense? Surely if each live is working independently, then it should read 415v(ish) across any pair? We measured the voltage all over the system, before the fuses (and checked fuses), before the meters, on the board before master switch, after it, before and after breakers, before and after isolators and on machines. Its the same result everywhere. We tried swapping the breakers, using the 20A on the tyre machine, that still does the same buzz but no movement.
I find it almost impossible that both machines have gone together, they have worked perfectly for a long time and nothing has been touched or changed. The whole installation is only 9 months old, all new wiring, board, breakers etc.
If the compressor did break, could it cause a fault on the board besides the breaker, and if so could it then affect the other breaker or other machine? None of the 240v is affected.
We are at a loss! We have no other 3 phase gear to test, and the shops are currently closed so can't try new breakers. The main thing bothering me is the L1-L3 being 0v, could a substation have a fault? But each live is still 240v?
Please help! Lost out on a day of business saturday and due to re-open tomorrow with no working machines!
Many thanks, Rich.
p.s I have pics and videos of equipment working (or not) if it helps.
I have a small industrial unit with three phase and single phase installed. The single is obviously for lights, standard sockets, phone, computer etc and is working perfectly.
The three phase supplies a tyre changer (10A breaker) and an air compressor (20A breaker).
Friday night they both worked fine, and as always I turned off the isolators and went home. Saturday morning, I came in, turned on the air compressor isolator and instead of firing up, the motor buzzed for a few seconds and tripped its breaker. Turned on the tyre machine and tried the motor, it too just buzzed but would not move, it buzzes without tripping the breaker. All 240v stuff continues to work.
I reset the compressor breaker, same result - buzz and trip. Same time after time.
I looked into the board, all the 3 incoming tails measure 240v each. Across L1-L2 its 425v, across L2-L3 its 425v, across L1-L3 its 0v. Does this make sense? Surely if each live is working independently, then it should read 415v(ish) across any pair? We measured the voltage all over the system, before the fuses (and checked fuses), before the meters, on the board before master switch, after it, before and after breakers, before and after isolators and on machines. Its the same result everywhere. We tried swapping the breakers, using the 20A on the tyre machine, that still does the same buzz but no movement.
I find it almost impossible that both machines have gone together, they have worked perfectly for a long time and nothing has been touched or changed. The whole installation is only 9 months old, all new wiring, board, breakers etc.
If the compressor did break, could it cause a fault on the board besides the breaker, and if so could it then affect the other breaker or other machine? None of the 240v is affected.
We are at a loss! We have no other 3 phase gear to test, and the shops are currently closed so can't try new breakers. The main thing bothering me is the L1-L3 being 0v, could a substation have a fault? But each live is still 240v?
Please help! Lost out on a day of business saturday and due to re-open tomorrow with no working machines!
Many thanks, Rich.
p.s I have pics and videos of equipment working (or not) if it helps.