Discuss Time delayed RCD in the UK Electrical Forum area at ElectriciansForums.net
My guys were testing a 500ma time delayed RCD today with our Fluke tester, can’t remember the model, 1556???
I had a go and couldn’t get it to trip either. The tester was set to time delayed setting, 500mA, did the 30s countdown but didn’t trip. Am I doing something wrong?? And yes I was definetly testing the load side of the RCD!?
Had you it set to the correct type of RCD, i.e. you weren't DC saturating an AC RCD or something like that?
Try it on the circuit not at the terminals. I can’t remember but there was one or two brands that don’t like being tested at the terminals...I don’t know the reasoning behind it, but worth a try.
It's memshield 2 MR30 RCBO pods which can't be tested from the terminal screws because the live sensing coil is on the pod which clips on above the terminal.
Reply to Time delayed RCD in the UK Electrical Forum area at ElectriciansForums.net
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...