Trey

In my AHU panel I have a transformer connected into the star/delta circuit (First time I've seen this) the original transformer was a 37kw with 415v 70% 60% 40% and star
tappings, this transformer is now faulty so I have ordered a new one which arrived today.

The problem is, on the old transformer the star points were connected seperately (one for each phase) which then went to the star contactor but the new transformer has the star connections connected together, is this correct? does this now give the circuit two star points? does this make any difference at all? do I have to do some modifications in the wiring?

Thanks for your help
 
Post some drawings or photo’s. I can’t make head nor tail of what you describe. You give no information regarding voltage. Is this a star delta motor? Nothing makes sense.

The manufacturer would be the best to ask.
 
Aah, not just me being thick then Tony.


Just try going on to international engineering sites and make sense of Joe from the corner pub in Jakarta wanting to wire a 275/33KV 150MVA transformer in his back yard in to the grid. You have to have a sense of humour.
 
Just try going on to international engineering sites and make sense of Joe from the corner pub in Jakarta wanting to wire a 275/33KV 150MVA transformer in his back yard in to the grid. You have to have a sense of humour.

Thanks Matey but way my head is, I think i'll leave that to you. :crazy:
 
Last edited by a moderator:
Great! Thanks for sharing your solution. When the next guy comes for similar help we'll know which expert to send him to now!

:50:

I'm not very clued up when it comes to Star/Delta so I thought the safest option was to give the job to a more senior electrician. I deal more with the domestic side, I don't know what the out come was as I'm only back to work in two weeks.

Anyway what I was asking was this is the drawing of the Star/Delta circuit with the old transformer

Star Delta 3.jpg

And this is what it would have looked like with new transformer

Star Delta 4.jpg

Would this work? Doesn't seem right to me, just curious!:49::49:
 
Could this be a Direct On Line connection and they are using the transformer instead of a Drive? Its a very old panel!
 
Thank you very much for your help Tony I had never heard of this before.

No I didn't connect anything (Past experience has taught me if you don't know what you doing leave it!) As I was not sure at all what I was dealing I asked the other electrician who has more experience with three phase to take over.

Once again thank you for the link
 
Seems to me the star link outs on top of the star contactor are duplicated at the tranny.
Made me chuckle when i saw your forum name as have missed it up to press but reading this post i think you'd be a tad wise to call it a transformer instead of tranny, not normally a issue but with your tag name its food for thought .......(no offence intended, top name choice lol) :)
 
Just had a 2[SUP]nd[/SUP] look at the first drawing, that’s wrong as well. The main contactor and O/L’s are in the wrong place.

I’ll do a new drawing and a description of the sequence in the morning. (With my insomnia, read about 4am).
 
Sod it, I can’t get to sleep!

View attachment 9100

There are two types of autotransformer starters and to add to the confusion they are wired the same. The sequence and the transformer construction are different.

The standard starter is open transition where at the change over from start to run there is a brief moment when no power is supplied to the motor. This can cause mechanical stress to the motor and load.

The Korndorfer starter is closed transition, so no loss of power at change over. Because of this the transformer has to be a bit more “beefy”. But because there is no break in the supply to the motor there is no mechanical stress.

Standard starter, open transition:
contactors 1 and 3 close. Giving a reduced voltage to the motor
time delay
contactors 1 and 3 open
small time delay (no power to motor)
contactor 2 closes. Giving full power to the motor

Korndorfer starter, closed transition:
contactor 3 closes
small time delay
contactor 3 closes. Giving a reduced voltage to the motor
time delay
contactor 3 opens. The transformer is now acting as a choke
small time delay
contactor 2 closes. The transformer is now shorted between it’s incoming and % tappings. But as it's the same potential bewteen the two points there is no current flow
small time delay
contactor 1 opens.

As can you see the sequence for the Korndorfer puts stress on the transformer where it has to withstand acting as a choke. So for small motors it’s uneconomical.
 
Last edited by a moderator:

Reply to Transformer in Star/ Delta connections in the Canada area at ElectriciansForums.net

Similar Threads

Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
734
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
381

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock