Hi, need some advice on a TT earth path.

House has CU in hall and a smaller CU in garage which is supplied with 6mm T&E from a 32A MCB in the house, the earth rod is connected into the garage CU then the cpc from the 6mm routes this into the house CU, is this OK or should I get the rod connected direct to the house CU?

Everything protected by 30ma RCD's as required by regs for TT, the only other observation was garage CU earth connects to gas pipe (in garage) & house CU earth connects to water pipe.

Thanks.
 
The submain is new and the house CU is older ? - so how was it earthed before the sub main was put in?

If i understand what you are saying then you effectively have the main protective bonding conductor from the water and the earth from the house CU, running into the 4mm(?) cpc in the 6mm T&E !!! This does not comply with BS7671. Min size for a main protective bonding conductor on a TT is 6mm and is governed by reg 544.1.1

Sounds like some changes are needed.

Where are the RCDs positioned?

Are you sure there is no earthing arrangement at the main cutout and the submain has not just been given a separate TT?
 
House is only TT, right more info, CU originally was in garage, Tails extended into house and split load CU installed, existing garage CU reused to supply garage, feed for this is the 6mm T&E coming from the new CU.

Earth rod is original with 4mm conductor to the garage CU, basically the garage CU earth bar is being used as main earth terminal. This then feeds into the house CU using the 2.5mm cpc in the 6mm feed. BS7671 542.3.1 states that a TT size need not exceed 2.5mm when RCD's are used, all feeds are protected by RCD's in the house CU, nothing is unprotected.

Protective bonding is 6mm, gas pipe to main earth terminal in garage, water pipe to earth bar in house CU

Any thoughts?
 

Reply to TT Earth connection question in the Australia area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
537
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
863
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock