Hi I've been testing a garage installation and the house is quite remote and has a tt supply. The supply to the garage is swa supplied via a 32a mcb on a 30mA rcd main switch. The earth spike resistance is 21ohms. The earth fault loop impediance at the main switch is 22.1ohms. At the garage it is 22.1ohms.
The rcd is tripping within the parameters but I feel the results are way to high but I've been told its just how far away from the transformer the house is. Anyone got any suggestions
 
Hi I've been testing a garage installation and the house is quite remote and has a tt supply. The supply to the garage is swa supplied via a 32a mcb on a 30mA rcd main switch. The earth spike resistance is 21ohms. The earth fault loop impediance at the main switch is 22.1ohms. At the garage it is 22.1ohms.
The rcd is tripping within the parameters but I feel the results are way to high but I've been told its just how far away from the transformer the house is. Anyone got any suggestions

Why do you feel the test results are way to high?
 
Is this a new installation of the earth electrode or an existing installation?
What work have you done?
What are the previous test results if the installation is existing?
What makes you say that the results are way too high?

Distance from the substation won't have any impact on the Ra, but will have a minute effect on Zs.

An Ra is acceptable if it is stable at that value. In theory any value could be acceptable as long as it is stable and meets the Zs requirements for the RCD.
But you should always get the Ra as low as possible.
 
Existing House we re-used the garage supply (garage got knocked down and a new one built) we then installed a 4 way consumer unit with sockets, lights, roller door etc in the garage
existing house db with rcd protection and 2 earth spikes with pit cover.
 
Domestic tt installations are not something I come across a lot. Most tt systems I do are on building site generators were the earth spike result can be 100ohms but the zs at the db of the generator is 0.02 ohms etc due to the generator
 
Domestic tt installations are not something I come across a lot. Most tt systems I do are on building site generators were the earth spike result can be 100ohms but the zs at the db of the generator is 0.02 ohms etc due to the generator

Generator installations are not TT and 100ohms is not acceptable for a generator installation
 
Generators are not my strong point !
Ive always been told to mark them as tt although the neutral/earth is linked inside
also been told cause it's got rcd protection the earth spike must be under 200 ohms !
 
Generators are not my strong point !
Ive always been told to mark them as tt although the neutral/earth is linked inside
also been told cause it's got rcd protection the earth spike must be under 200 ohms !

Utter nonsense!
A generator with a N-E link referenced to earth is a TNS earthing system.
Ask whoever told you this to show you the regulation which says that the limit is 200ohms for a TT or TNS earth electrode!
 
Maz ze should be 0.8 ohms ?
Whats the maximum valve allowed for the spike

That's for a DNO supply, not a generator! You will struggle to get that on a generator due to Zgen. But Ze has nothing to do with the earth electrode on a generator, it's not in the fault loop!

There is no maximum value set for the earth reference, it's pretty much outside the scope of bs7671 and more in the realms of various earthing standards.
20ohms is often suggested as this is the theoretical max for a TNS at a substation
 
You will love this One. Years ago our supervisor made another tradesman get the value under 200 ohms on a site being supplied via a big generator. They couldn't get the value down so they ennded up getting old crash barriers buried to try and get under the 200 ohm value. So basicly the earth spike is just protecting the generator frame and needs no value recorded ?
 
You will love this One. Years ago our supervisor made another tradesman get the value under 200 ohms on a site being supplied via a big generator. They couldn't get the value down so they ennded up getting old crash barriers buried to try and get under the 200 ohm value. So basicly the earth spike is just protecting the generator frame and needs no value recorded ?

The earth spike isn't protecting anything. It is providing the earth reference for a TNS supply. It ties the neutral point of the generator to the potential of the earth.
 

Reply to TT earth results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
482
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
875
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock