Discuss TT System RCD protection in the UK Electrical Forum area at ElectriciansForums.net
C
charliefarli
Hello electrical mafia, Just a quick one for you on this fine evening…..been asked to do the electrics for a hot tub install, house is a TT system and has no upfront RCD the ZE reading is 12 ohms. Would I be ok to split tails in a henley block and feed hot tub from a garage unit that has a 30ma RCD main switch or does an upfront 100ma need to be fitted to whole install swell as this. I haven't had much experience of TT systems and thought I would ask the finest bunch of sparks about for there wisdom.Thanks
Thanks for the reply,really appreciate it.The guy used to be my accountant and is tight as aresholes,lol!!Can you get away with just the 30ma RCD on the garage board and no upfront protection if just putting a test on the hot tub circuit?and make a note on test it is recommended that upfront rcd is put in for whole install?
Thank you for reply.I would of deffinetly done that but the main board is choca block with no spare ways, sorry i should of added that before. So a 100ma Upfront RCD is not needed because all circuits are protected by 30ma RCDS?Is this correct?
Yes but its also not a bad idea to have a 100mA time delayed up front. You could install the 100mA in the tails to provide a single point of isolation. Out of this to a double pole Henley block then feed existing board and new board...alternatively talk the customer in to a new board.
Great reply, thank you. I am afraid this customer is one of those, "get it done the cheapest possible as long as its working" mob! I will advise him but am sure he will say no when I say it is not a necessity. So 100ma upfront RCD's are not needed on TT systems if all circuits are already protected by 30ma RCD's via the board but it is good practise and advisable to do so?
Yes as provides as a back up when relying on an RCD as I doubt any customer ever tests their RCD quarterly..also with dual RCD amendment 3 boards the 100mA S type provides protection for the flexible links feeding the RCDs.
Morning everyone, No the board there is not amendment 3 but has dual RCD'S so is earlier 17th board. There is one circuit that has been put on the main switch which is a 16mm t and e on a 50 amp breaker which feeds a massive outhouse, there must be a junction box on the outside wall which converts it to armoured unless it goes through a ducting. This should be protected though and I will be advising customer its unsafe and if he refuses to put up front RCD I will mention it in test on comments on existing installation. The garage board I will be putting in will be amendment 3 metal Wylex board with a metal blank. Thanks all for your help, have a good day
Reply to TT System RCD protection in the UK Electrical Forum area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...