TT System with 31 ohm ze that drops down to 0.31 ohms when the bonding is all connected

Am I right in thinking that's because a house nearby has been converted to a tncs and they share a common bonded gas supply?
 
It’s not a Ze with the bonding connected, it’s a Zdb 😉

Parallel Paths. 👍
 
Electricity is like humans, it’s lazy and will always take the path of least resistance to get where it wants to go.

From what you’re saying, if the properties do share a common bonded gas supply, I’d imagine it’s using the neighbours tnc-s earthing arrangement via the gas bond when it’s connected.
 
Does it matter that the gas supply provides a better earth than the earth rod though.
A metallic service pipe will always provide a better earth than a rod due to its much greater physical contact with true earth.
In a fault would it just use the gas pipe as opposed to the rod
In a fault situation electricity does,nt use one path as opposed to another.It uses EVERY path that's available.We are all accustomed to hearing "the path of least resistance" when in reality its "every path "
 
Does it matter that the gas supply provides a better earth than the earth rod though.
No, but service pipes cannot be relied upon as next plumbing job, etc, could change it to plastic.

So even if the bonded Zs is low enough for OCPD-based disconnection, you still need the RCDs and a rod capable of reliable ADS without the bonding in place.
 
No, but service pipes cannot be relied upon as next plumbing job, etc, could change it to plastic.
And this is the problem that is often forgotten on installations like this

The other problem is the simplistic approach many take to earth rod installation without having any understanding of how to optimise the installation to get the best result. The general approach of a 4ft rod will do doesn't really cut it in all cases and there are times when an 8ft or 12ft rod or multiple linked rods gives the optimum result, but this all comes back to training and when the approach of some is that domestic is only a few wires the reality of complex earthing issues hits and then it takes some skill to pull the resistance down

So even if the bonded Zs is low enough for OCPD-based disconnection, you still need the RCDs and a rod capable of reliable ADS without the bonding in place.
Metal gas and water pipes were never intended to be an earth and the bonding was always intended to protect those carrying out maintainance on the external pipework from stray voltages / currents from properties on the network
 
The other problem is the simplistic approach many take to earth rod installation without having any understanding of how to optimise the installation to get the best result. The general approach of a 4ft rod will do doesn't really cut it in all cases and there are times when an 8ft or 12ft rod or multiple linked rods gives the optimum result, but this all comes back to training and when the approach of some is that domestic is only a few wires the reality of complex earthing issues hits and then it takes some skill to pull the resistance down
Very much so!

Getting a good and reliable earth "rod" is far harder than most folks realise. I am luck at our site in that it is fairly moist clay all year once you are down by the 30cm or so tarmac-ish layer (site is only 10m above nearby river) but even for that I used 2m rods as the top layer drying out in summer, or freezing in winter, has a massive impact on conductivity.

Once you discount the top 2 feet or so as unreliable for moisture you see why a 4 foot rod is asking for trouble.
 
Metal gas and water pipes were never intended to be an earth
Valid point.The idea of currents flowing along a gas pipe never sounds right.Risk of arcing.
and the bonding was always intended to protect those carrying out maintainance on the external pipework
That will work when carrying out maintenance on internal metalwork.Such as changing a metal gas boiler.The Cross bonding serves that purpose.

On external pipework however the housebonding is of no value when it comes to working on metallic services.For protection in these circumstances maintenance crews need to "cross bond" wherever the metal services are been cut by connecting a copper loop across the cut
 

Reply to TT with low ze when bonding connected in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock