Now I understand that this question may seem pointless, so humour me anyway...

A lady had underfloor heating installed about 10 months ago along with her new kitchen...

I was there for the kitchen install but didn't do the mats, there are two mats serving her kitchen and utility room, both are connected to the same programmer....

after she had issues with 'overloading', as she was 'reliably' informed, the mats were disconnected...

anyway ive had a look and it is in fact a L-E fault on just one mat... so connected one back in and its all good with a reading of >999 from L+N-E

the other mat has a reading of 0.01 megohms and 17,000ohm for continuity from L+N-E....

she was sold a new programmer by the company as i passed this info on to the person who has taken responsibility for the install, and they called the technical support - who told him the readings are normal and that a new programmer at £80 was required....

Anyway this mat trips the RCD obviously, but with a continuity of 17k if it was connected to just an MCB it would have a fault current of 13mA? and therefore the mat would work again?
 
any reading below 1Mohm is a fail, so i'd not even connect it to a duracell. condemn the mat. leave disconnected. end of.
 
  • Like
Reactions: 2 people
yep fair enough, have called technical support and they will send a new replacement mat, but that cost is substantially outweighed by the labor cost of lifting and replacing all her nice expensive floor tiles... hey ho not my kitchen though!
 
Just a thought you wasnt testing the floor probe was you? The range from 8K ohms upto 25k ohms - but i guess the floor probe wont have an earth wire.
 
na, nice thought though.. the 2 mats hit a jb before entering the programmer, i isolated the mat at the jb, so not the probe.... i agree with the tech bloke tho, its weird it worked fine for 6 months then one day POOF
 
They do - it doesnt take much to nik the cable then with the heating and cooling it just gives up. Plus some cable mats have very little insulation to protect them.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Underfloor Heating
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
ultinator,
Last reply from
dansk,
Replies
5
Views
1,243

Advert