When installing a new circuit for a pv system it is neccessary to fill in an installation cert. If the earthing can not be verified is it then neccessary to install new 10mm earth wires to gas and water mains or ok to note it on the sheet? Iv'e been replacing earths up to now but this job is sometimes more time taking than the installation itself. What do you guys do?
A long lead can verify if it's within.05 of an ohm but is that good enough?
Yes, an EIC is required for a new circuit, along with a schedule of items inspection and schedule of test results.
131.8 - Additions and alterations to an installation
No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate.
Gas and water pipework could read as low as 0.05 ohms between your testing point and the MET due to connections at the boiler.
Reply to upgrading of earthing. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Shop with no earth coming from head, overhead lines in sight everywhere - definitely no earth from the DNO. Two 10mm earths going into the DB...
I know PV installers sometimes use SWA to carry DC into the house especially when the PV is ground mounted. Can anyone help me understand the...
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...