Are you talking about the options on a test device such as a mft?
If so, Z line measures the impedance Z of the lines R1 + Rn for phase to neutral, and R1 + R1 for phase to phase (depends on your connection)
Z loop measures the impedance of the earth loop - R1 + R2 (line and earth connection)
Or is the OP asking why such tests are done?
If so, the Z-loop test is to prove the fault current in the event of phase-earth short is sufficiently high to operate the over-current protective device (OCPD) fast enough to have an acceptably low risk of electric shock, or conductor overheating. In a typical UK case (230V, TN system) the "fast enough" is 0.4s for most circuits, 5s for some feeders, etc.
The Z-line test is done as well so the higher of the two prospective fault currents can be recorded, and compared with the ratings of equipment to establish that in the event of a short the OCPD and/or switch-gear can safely interrupt it.
More of a basic question like, "Why do we do a Z-line or Z-loop test?"
As said by pc above, there are two basic reasons, firstly to ensure the impedance is low enough that sufficient current flows in the event of a fault and therefore will operate the protection within the required disconnection times.
Secondly, to determine how much current could flow as a maximum, to ensure that the fault level is not higher than the equipment can withstand or open where appropriate.
There are two basic possibilities, a fault involving earth, and a fault between phases or phase and neutral therefore both have to be checked
Reply to What is a Z-line and Z-loop test? in the UK Electrical Forum area at ElectriciansForums.net
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
I am in UK and have just built a summerhouse and inside is a large LG flatscreen TV. I purchased an aluminium pole, ran the cable out and up...
Confused as to what the earth fault loop is. I'm aware it's the path that fault current takes (Line-Earth) but how many times does fault current...
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...