What's the benefit over installing it in the workshop?
 
I need 2 supplies. One for the workshop and another for a conservatory/utility extension. And it would avoid going through the wall into the existing CU - I want to split the tails in the box to the new one.
I can't see any reason for not doing it that way myself.
 
It's better to mount it inside where it will be better protected from the elements


Why does a utility room extension need a new supply? Are there not circuits already there you can extend?
 
Hi Guys (and girls),
Can anyone come up with a reason not to fit a 2 way consumer unit into an outside meter box to supply a workshop extension?


Other than a main switch fuse for extended tails or split tails, i don't think the DNO would be too happy having a CU housed in their provided space....
 
  • Like
Reactions: 3 people
Other than a main switch fuse for extended tails or split tails, i don't think the DNO would be too happy having a CU housed in their provided space....

Same as ^^^^^^^
 
If the meter box is large enough that you could fit your own board in there they would be happy enough, but the dno don't allow customer equipment on their board. So if it's a normal size cabinet with only room for a DNO board the CU will need to go inside.
 
Other than a main switch fuse for extended tails or split tails, i don't think the DNO would be too happy having a CU housed in their provided space....

On my recent meter move the DNO allowed our switch fuses in place of DNO double pole isolation switches to free up a bit of room. But they would not allow the switch fuses on their board, if the cabinet had been too small the tails would have had to run through the wall with the switch fuses internal.
 
On my recent meter move the DNO allowed our switch fuses in place of DNO double pole isolation switches to free up a bit of room. But they would not allow the switch fuses on their board, if the cabinet had been too small the tails would have had to run through the wall with the switch fuses internal.

That would kinda defeat the whole point of having a switch fuse if the tails are over 3 metres. If that was the case i'd be having a few words with the DNO's Area Engineer, rather than listening to the meter installer.
 
  • Like
Reactions: 1 person
Hi Guys (and girls),
Can anyone come up with a reason not to fit a 2 way consumer unit into an outside meter box to supply a workshop extension?

Not the best solution but seen it done before. You could install another OMB next to the existing OMB and house a suitable 2 way unit within something like a garage unit to increase IP rating.
 
That would kinda defeat the whole point of having a switch fuse if the tails are over 3 metres. If that was the case i'd be having a few words with the DNO's Area Engineer, rather than listening to the meter installer.

No. Tails would have been less than 3 meters with switchfuses internal so not defeating object at all..

Meter installers were not involved at any stage of the supply move, the DNO dealt with both fitting the new cable, cut-out and moving the meters from their old position.

And I am correct that they would not allow customers gear on their board. With the DNO not fitting double pole isolators they were able to use a smaller board, but we had to fit our own seperate board for the switch fuses.

This was SEPD. Other DNO's may have different policies.
 
Reason given for not installing equipment with DNO's is that there is quiter a high occurence of burn back from metering equipment (Cut Out) etc. If your equipment is in same enclosure it can become a chicken and egg situation, whose equipment caused the fire/burn back ?. Cheaper staying away from there equipment than legal fees ?.
 
  • Like
Reactions: 1 person
No. Tails would have been less than 3 meters with switchfuses internal so not defeating object at all..

Meter installers were not involved at any stage of the supply move, the DNO dealt with both fitting the new cable, cut-out and moving the meters from their old position.

And I am correct that they would not allow customers gear on their board. With the DNO not fitting double pole isolators they were able to use a smaller board, but we had to fit our own seperate board for the switch fuses.

This was SEPD. Other DNO's may have different policies.

You only need ONE switch fuse, and as far as i'm aware, these can be fitted into DNO cut-out/ meter cabinets. The buggers should be fitting DP isolators as standard/matter of course anyway!! All this crap about too expensive, ....what's the standing charge for, if not for supply maintenance and improvement work...
 
  • Like
Reactions: 1 person
Basically in the past it was not practical to fit anything else on Elecy Board meter boards (internal or external OMB's). Board was solely for their equipment and additional equipment if so required at a later date. Typically E7 metering Time clock and or check meters when being monitored.
The Elecy Board personal where told , never interfere with customers electrical installation. If the job couldn't be done because someone had fitted a con-unit or something similar onto the board......Job stopped. Up to the customer at their cost to employ an electrician to remove it.
 
You only need ONE switch fuse, and as far as i'm aware, these can be fitted into DNO cut-out/ meter cabinets. The buggers should be fitting DP isolators as standard/matter of course anyway!! All this crap about too expensive, ....what's the standing charge for, if not for supply maintenance and improvement work...

Isolator one thing, as we know makes life easier to isolate the supply 100%. Switch fuse in there I'm not so sure.
 
Reminds me of a job that i went to when working for a DNO. 3 phase flush OMB was installed in a stone wall as per spec in readiness for the DNO 3 phase u/g cable to go into. Got on site,opened the 3 phase door only to discover a 3 phase metal clad switch fuse in there! It completely filled up the box! God knows what the electrician was thinking off. Needless to say....he had to remove it.
 
Isolator one thing, as we know makes life easier to isolate the supply 100%. Switch fuse in there I'm not so sure.

A switch fuse to protect extended tails is more for their benefit than the customers installation. I've not heard of a DNO not allowing a switch fuse to be mounted in an external cut-out cabinet!!
 
You only need ONE switch fuse, and as far as i'm aware, these can be fitted into DNO cut-out/ meter cabinets. The buggers should be fitting DP isolators as standard/matter of course anyway!! All this crap about too expensive, ....what's the standing charge for, if not for supply maintenance and improvement work...

This was a 3 phase move for 3 flats with one flat having economy seven and 2 meters/supplies. As I have already stated, SEPD were happy with customer gear inside the enclosure, but not on their boards. The installation literature provided was also clear about this. The switchfuses were fitted in lieu of the double pole isolators.

So in fact switchfuses were required
 
This was a 3 phase move for 3 flats with one flat having economy seven and 2 meters/supplies. As I have already stated, SEPD were happy with customer gear inside the enclosure, but not on their boards. The installation literature provided was also clear about this. The switchfuses were fitted in lieu of the double pole isolators.

So in fact switchfuses were required

That's fine if the cabinet/enclosure is of sufficient size to accommodate the extra devices. I'm just trying to think of a typical Cabinet/enclosure where it would all fit in, not using the back fixing boards that usually take up the whole rear of these enclosures... must be a bloody big cabinet to contain a 3 phase cut out and all those meters and switch fuses etc!! Got a photo??
 
That's fine if the cabinet/enclosure is of sufficient size to accommodate the extra devices. I'm just trying to think of a typical Cabinet/enclosure where it would all fit in, not using the back fixing boards that usually take up the whole rear of these enclosures... must be a bloody big cabinet to contain a 3 phase cut out and all those meters and switch fuses etc!! Got a photo??


You are correct, the enclosure is a large IP55 metal 1m x 1m box, although the dno were happy for me to 'build' my own enclosure if necessary. A standard plastic outdoor enclosure would typically only contain one board(the DNO's) and any switchfuses would have to be mounted internally within the DNO's 3m tails limit, ensuring the tails do not run through the cavity.

This is why I have suggested that it is likely the OP will have to mount his CU internally unless he has an overlarge meter cabinet large enough to contain his own board.


I'll have a look see if I can get a photo up, as I have another thread running about conversion to a tncs head for the installation.
 
DNO I worked for would never allow 3rd party equipment on their board. However when taken over by another DNO it was allowed. New DNO would allow those 60amp MEM switch fuses which were compact to be fitted usually top right hand corner.
 
That's fine if the cabinet/enclosure is of sufficient size to accommodate the extra devices. I'm just trying to think of a typical Cabinet/enclosure where it would all fit in, not using the back fixing boards that usually take up the whole rear of these enclosures... must be a bloody big cabinet to contain a 3 phase cut out and all those meters and switch fuses etc!! Got a photo??

Been trying to upload a photo but cannot for the life of me work it out!!!!!!!!!!!
 
That would kinda defeat the whole point of having a switch fuse if the tails are over 3 metres. If that was the case i'd be having a few words with the DNO's Area Engineer, rather than listening to the meter installer.
I concur. My switch fuses nearly always go next to the cut-out
 
Are you not meant to have 1 point of isolation? If con-unit indoors, then 2 way unit fitted in OMB that creates 2 x isolation points. I know done like that years ago with several con unit/ sw/fuses installed by the meter position.
 
A switch fuse to protect extended tails is more for their benefit than the customers installation. I've not heard of a DNO not allowing a switch fuse to be mounted in an external cut-out cabinet!!

The sunny boys have cramped all their equipment inbox, meter an all. lol
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Exeter - a glorious place to live!
Business Name
Mike Willmott

Thread Information

Title
Workshop Supply
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
willy fixit,
Last reply from
7029 dave,
Replies
25
Views
3,001

Advert