Discuss Ze results in the UK Electrical Forum area at ElectriciansForums.net
Hi iv been doing Ze reading and just wondered if the Ze reading you get at the main DB directly from the (lucy)
Is the same Ze that you would put on the certificate for sub board further in the installation.
As Ian just said - Ze = external, so everything and anything else is the external plus the resistances of the circuits = Zs = sum of them all.
Reply to Ze results in the UK Electrical Forum area at ElectriciansForums.net
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...