Discuss Cable run for Fixing a double socket on Chimney Breast in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
14
Hi

Would this be allowed : Fitting a double socket to a chimney breast , chased a horizontal run across the chimney breast then to the first corner then along horizontal to about 500mm to meet up with a double socket feed that comes down to a double socket and then it follows that run down into that back box to pick up the feed .

The cable is in a oval plastic conduit and will be just below the surface , the house has RCD protection .

Spike
 
i would come horizontally from existing socket onto chimney brest, then vertically to your new socket. makes the safe zones easier to follow. or....... up from existing socket int ceiling void, then across to chimney and verticall down to new socket.
 
Technically the 500mm you chased horizontally to meet the vertical chase would not be in the zones.
I have drilled diagonally through the chimney breast wall before to make the horizontal chase on the face of the chimney meet the vertical chase on the side. The walls are more than thick enough to avoid going into the chimney cavity quite easily.
 
Thanks for the feedback, just a note , the chimney breast is flush with the wall ! .
Cheers
spike
then either way is compliant.each socket will create a safe zone for the cables.
 
Maybe this will explain it better !

Socket Fireplace.jpg
 
Be careful not to puncture the chimney in any way. Ifs it's not an active chimney now then it may well become active in the future and could leak harmful gases.
 
If it is going to be a non complient circuit , then there is no need to go there .
Would you need to Meggar a 4 mtr length of new cable that goes from one double socket to another ! .
Spike
Non compliant with what? There is always a need for testing how else do you know it’s going to be a safe installation? and you should carry out more tests than just IR. continuity of bonding conductors CPCs, Polarity, PFC, Ze, Zs, RCD trip times excuse me for being an a**e I didn’t realise you were qualified till I looked at your profile just there...
 
Last edited:
Non compliant with what? There is always a need for testing how else do you know it’s going to be a safe installation? and you should carry out more tests than just IR. continuity of bonding conductors CPCs, Polarity, PFC, Ze, Zs, RCD trip times excuse me for being an a**e I didn’t realise you were qualified till I looked at your profile just there...
Hi
I don't need to mention doing basic tests like , Polarity /continuity etc , it goes without saying that you would do those checks ! , it is just a very simple wiring job , I can nearly touch each end of the cable with both hands ! .
 
Hi
I don't need to mention doing basic tests like , Polarity /continuity etc , it goes without saying that you would do those checks ! .
Sorry as I said I didn’t realise you were a spark until I checked your profile. Lots of people come on here wanting advice on things like this and don’t have a clue or any test gear.
Have you not got anOSG? The safe zones are pretty well explained in there.
 
Is this an old house? Chimneys tend to be sticking out from the wall, so you might find the area of wall to the left and right of the chimney actually plasterboarded over alcoves.
Is the socket for a wall mounted TV? Do you need to also find a cable route for the AV cables?
 
Hi
I don't need to mention doing basic tests like , Polarity /continuity etc , it goes without saying that you would do those checks ! , it is just a very simple wiring job , I can nearly touch each end of the cable with both hands ! .

Even though it's a short run it will still need to be tested properly. As you should know, even a small section damaged can deem it unsafe
 
Is this an old house? Chimneys tend to be sticking out from the wall, so you might find the area of wall to the left and right of the chimney actually plasterboarded over alcoves.
Is the socket for a wall mounted TV? Do you need to also find a cable route for the AV cables?

Hi
Yes it is a old house and yes it is for a wall mounted TV , the whole wall is solid brick , AV cables n Sky etc coming in from opposite wall .
Cheers
Spike
 
I'm lost.
AV coming from opposite wall? In the same room, or the room behind the chimney?. Can the power come the same route?
Are you drilling right through the wall? Beware of the path of the chimney, it might start off central to the fireplace but veer to one side just above. I (recently did the same job, tried to drill into chimney for TV cable route and missed)
 
Even though it's a short run it will still need to be tested properly. As you should know, even a small section damaged can deem it unsafe[/QUOTE
I'm lost.
AV coming from opposite wall? In the same room, or the room behind the chimney?. Can the power come the same route?
Are you drilling right through the wall? Beware of the path of the chimney, it might start off central to the fireplace but veer to one side just above. I (recently did the same job, tried to drill into chimney for TV cable route and missed)

Sorry ajacent wall
 
Getting your opposite and adjacent mixed up there? Trigonometry not you strong point?

Well I am a little older than you I guess , not really worked in the trade for roughly 20 years or so , so a little relapse now and again in spelling etc is inevitable :).
Actually I was quite good at Trig n Tech drawing in my younger days
 

Reply to Cable run for Fixing a double socket on Chimney Breast in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
933
Is it possible to install a double socket on a chimney breast that has an active wood burner at the bottom? Looking to mount a TV above the...
Replies
1
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
271
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
946

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock