If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Ok own up who's done this?

I try my hardest to never do this but have, on very rare occasion installed meter tails in a cavity as the lesser of evils.

Would be interesting to hear real world thoughts on this and potential work arounds so you don't have to. I know someone on here posted a while back about some sort of capping that you could put over the tails so they couldn't be drilled. Not entirely convinced about that although I've not had a proper look at it in real life.

I had one recently where the meter box was on external wall and I needed to run an armoured from there to an internal consumer unit. Went to great trouble to avoid running the cable in the cavity and builder comes along and says why didn't you just push it up the cavity!
 
Can't see how it can be avoided?

My only issue with it, you can't see whats happening to the cable as its being installed, and unsupported over the distance.
 
  • Agree
Reactions: robd
Can't see how it can be avoided?

My only issue with it, you can't see whats happening to the cable as its being installed, and unsupported over the distance.
While I agree you cant see whats happening, then end you pull out should give you a idea that its not being damaged. As for supporting of it, its only the same as cables in vertical trunking, which dont get supported.
 
  • Agree
  • Like
Reactions: robd and 123
Whats your issue with running cables in a cavity?

UKPN don't like it and building inspectors often don't like it as you're bridging the cavity. Although quite what the insulation filling the cavity is doing if not bridging the cavity is anyones guess.
 
  • Like
Reactions: MFS Electrical
While I agree you cant see whats happening, then end you pull out should give you a idea that its not being damaged. As for supporting of it, its only the same as cables in vertical trunking, which dont get supported.

The cable is made up of its entire length, whats happening at its ends, doesn't necessarily suggest what has happened to the rest of it.

I though vertical trunking was required to have cable supports over certain lengths; was there some new reg or update on that in the last amendment.
 
  • Like
Reactions: Risteard
UKPN don't like it and building inspectors often don't like it as you're bridging the cavity. Although quite what the insulation filling the cavity is doing if not bridging the cavity is anyones guess.

Thing is though, if the meter box is on the outside and CU on the inside, it has got to go in the cavity some point, even straight through will bridge the cavity.
 
  • Agree
Reactions: robd
The cable is made up of its entire length, whats happening at its ends, doesn't necessarily suggest what has happened to the rest of it.

Well thats it, we cant run a cable through any wall at all then if thats the case, unless we completly dismantle it then rebuild it once the cables installed.
 
  • Funny
  • Agree
Reactions: robd and Zdb
Well thats it, we cant run a cable through any wall at all then if thats the case, unless we completly dismantle it then rebuild it once the cables installed.

Thing is though, if the meter box is on the outside and CU on the inside, it has got to go in the cavity some point, even straight through will bridge the cavity.

Now your just being silly. I have and will install such cables in a cavity, but you have to bear these points in mind.
 
Thats exactly my point, use your professional judgement as to weather any damge to the cable is occuring.

The potential damage to the cable, is a bit of a shot in the dark though (if you excuse the pun).
 
Thats exactly my point, use your professional judgement as to weather any damge to the cable is occuring.
what's the weather got to do with it?
 
  • Funny
Reactions: robd and Dillb
Isn't the issue with bridging the gap so that water doesn't transfer from the outside wall to the inside wall?
You can stop this by installing the cable at an angle, so the water can't run down the cable to the inside wall. This is of course for installing the cable virtually horizontal.
 
Think its the suggestion of such cable running vertically in the cavity, that allegedly can cause water breaching the cavity.
 
  • Like
Reactions: DPG
If the cavity is subsequently filled with insulation, the current carrying capacity of the cables will be significantly reduced.
 
If the cavity is subsequently filled with insulation, the current carrying capacity of the cables will be significantly reduced.
Thats like wiring a conservatory and putting sockets on the wall attached to the house, they will need to be IP rated incase they ever take the conservatory down.

You can only allow for what is there when installing.
 
Thats like wiring a conservatory and putting sockets on the wall attached to the house, they will need to be IP rated incase they ever take the conservatory down.

You can only allow for what is there when installing.
When working on the O2, we installed IP rated containment and accessories, just in case they ever removed the cover.
The fact that the internal structures are made from MDF not withstanding.
 
  • Funny
Reactions: Rpa07

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

mattg4321

Arms
~
Joined
Location
South East UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Meter tails in cavity
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
37

Advert

Thread statistics

Created
mattg4321,
Last reply from
Andy78,
Replies
37
Views
15,708

Advert