By saying no continuity do you mean low ohms measurement between MET and riser is off the scale (Im guessing greater than 200 ohms)

But insulation resistance between MET and riser is 0.00 Mohms.

Is that right? otherwise the information contradicts itself because no continuity wouldnt give a reading of 0.00 Mohms and maybe where the confusions is.
 
The key point of the original question I think is is there an exposed conductive part, a live part (even if covered), or another bonded extraneous conductive part within 2.5 m of the hatch giving access to the riser.
The majority of the riser is inaccessible and therefore cannot introduce a potential; if the access hatch is not near any conductive part that may become live and can be simultaneously touched by a person or livestock, then the part at the hatch will also not be able to introduce its potential into the installation and bonding would not be necessary.

I think what Ian1981 is saying about measurements is as described in the below diagram. The riser is connected to true earth, but not connected to the installation protective conductors.
Extraneous not connected to installation.jpg
 
  • Like
Reactions: Wilko and DPG
no i'm confused ( doesn't take much). in OP's post #4, he says:
Testing from the MET or rather the source of earthing to said pipe.
Main earthing conductor disconnected from source earth
IR set to 500v reading of 0.00 Mohms
Also no continuity between said pipework and a known earth source

so... riser is 0.00 M to MET and no connection to earth. that says it's not extraneous.?????
 
no i'm confused ( doesn't take much). in OP's post #4, he says:
Testing from the MET or rather the source of earthing to said pipe.
Main earthing conductor disconnected from source earth
IR set to 500v reading of 0.00 Mohms
Also no continuity between said pipework and a known earth source

so... riser is 0.00 M to MET and no connection to earth. that says it's not extraneous.?????
The OP has apparently changed his mind.
 
Maybe some of the wording wasn't clear. No need for things to get offensive though.
 
no i'm confused ( doesn't take much). in OP's post #4, he says:
Testing from the MET or rather the source of earthing to said pipe.
Main earthing conductor disconnected from source earth
IR set to 500v reading of 0.00 Mohms
Also no continuity between said pipework and a known earth source

so... riser is 0.00 M to MET and no connection to earth. that says it's not extraneous.?????
I think perhaps the post might be worded better as

Testing not from the MET but from the source of earthing, whilst it is disconnected from the MET, to said pipe.
IR set to 500V reading 0.00MΩ.

When testing from a known earth internal to the installation to the said pipework there was no continuity.


This is what has been said in post 19.

The pipe is (presumably) buried in the ground and so has very good contact with the ground and therefore shows up as an effective earth rod. However the pipe according to the continuity readings is not connected to the installations earth wiring i.e. it has not been bonded nor has it got a connection with any cpc.
Therefore the pipe is at earth potential but the issue is does it introduce that potential into the installation.
 
  • Like
Reactions: DPG
Therefore the pipe is at earth potential but the issue is does it introduce that potential into the installation.

or does it introduce an earth potential into the building? and if so, can it be touched? that seems to be the £64,000 question.
 
A "dry riser" is a vertical pipe that usually starts at ground floor level and has an outlet on each floor. Its purposes is to allow firefighters to connect at ground level and the fire level without having to run hose in stairwells.

At no point would it enter the "ground". Effectively, its just a bit of metal within the building. Unless someone has made some sort of connection, then I would be surprised if it tests as extraneous.
 
  • Like
Reactions: DPG
In relation to the OP i think @Devonchris is right and at no point should that dry riser be in the ground apart from fixed to it, but the OP is the man on the job and an experienced one at that.
 
could be explained maybe someone else in the building has already bonded it to their MET? making it an ECP for all other equipotential bonding zones it enters
 
could be explained maybe someone else in the building has already bonded it to their MET? making it an ECP for all other equipotential bonding zones it enters
Shut it down Marvo.
It's getting ridiculous.
 
The key point of the original question I think is is there an exposed conductive part, a live part (even if covered), or another bonded extraneous conductive part within 2.5 m of the hatch giving access to the riser.
The majority of the riser is inaccessible and therefore cannot introduce a potential; if the access hatch is not near any conductive part that may become live and can be simultaneously touched by a person or livestock, then the part at the hatch will also not be able to introduce its potential into the installation and bonding would not be necessary.

I think what Ian1981 is saying about measurements is as described in the below diagram. The riser is connected to true earth, but not connected to the installation protective conductors.
View attachment 43000
Didn’t realise it’s thread is still running but yes Richard you are correct
 
  • Like
Reactions: Richard Burns
I think perhaps the post might be worded better as

Testing not from the MET but from the source of earthing, whilst it is disconnected from the MET, to said pipe.
IR set to 500V reading 0.00MΩ.

When testing from a known earth internal to the installation to the said pipework there was no continuity.


This is what has been said in post 19.

The pipe is (presumably) buried in the ground and so has very good contact with the ground and therefore shows up as an effective earth rod. However the pipe according to the continuity readings is not connected to the installations earth wiring i.e. it has not been bonded nor has it got a connection with any cpc.
Therefore the pipe is at earth potential but the issue is does it introduce that potential into the installation.
Correct again
 
A "dry riser" is a vertical pipe that usually starts at ground floor level and has an outlet on each floor. Its purposes is to allow firefighters to connect at ground level and the fire level without having to run hose in stairwells.

At no point would it enter the "ground". Effectively, its just a bit of metal within the building. Unless someone has made some sort of connection, then I would be surprised if it tests as extraneous.
The dry riser comes out of the ground all metallic in construction and does introduce an earth potential.
It is a separate service entering the building and not in anyway connected to the main buildings water supply.
 
  • Agree
Reactions: Pete999
Shut it down Marvo.
It's getting ridiculous.
don't get it? was it a joke and I'm being thick or just you quoted the wrong post?
 
  • Like
Reactions: DPG and bigspark17
don't get it? was it a joke and I'm being thick or just you quoted the wrong post?
Agree!! If you dont like the post just ignore it!!
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Extraneous conductive parts
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
60

Advert

Thread statistics

Created
Ian1981,
Last reply from
Marvo,
Replies
60
Views
13,743

Advert