Discuss Bonding to gas and 544.1.2 in the UK Electrical Forum area at ElectriciansForums.net
T
The Ghost
Called today as client wanted boiler serviced/fixed. Gas safe man looked at meter boxed outside and said "No bonding! No fix!" Called me to assess. So...Clearly bonding x 2 are leaving the CU. Correct size. Test to water and Gas outside and readings below/within 0.05 ohms continuity. Suggesting there was indeed bonding connected as a previous electrician had confirmed the same. My consideration is looking at the above reg it says ...or at the point of entry to the building... Now how do you read that? Does it mean
A: the external point of entry
B: the internal point of entry
I have always assumed it is a matter of where it enters the building inside. Therefore, as in this case the bonding is probably connected under the floorboards inside the front living room as readings do indicate, and evidence of bonding cables leaving CU. What is your view?
Anyway it is clear that we must provide bonding to the outside gas meter so that work can go ahead and satisfy the gas man. Seems a bit silly to me but what else can you do.
I have this problem too Mr gas man can't see the earth so won't touch. To be fair it should be in an accessible position for testing and inspection as it's a mechanical joint in most cases! I took the point of entry to mean where it comes in so would say internal. Also if external not in the meter box it would need some protection from the weather and the thieving types that are a magpie for copper!
For me the point of entry for bonding is internal however my common sense tells me that if the pipe work is not readily accessible then as close to the point of entry using suitable clamps for the environment is acceptable and within the spirit of the regulations.
It's more nonsense where common sense goes out of the window, I did a CU change earlier this week, it was in the attached garage. The gas pipe [28mm copper] came in to the corner of the garage then up and along the length of the garage 300mm or so above the CU. So as it was continuous and with soldered couplers/elbows I thought do I run 8 metres of 10mm back to where the pipe enters or straight up to above the CU .....
I once ran a bonding cable from the CU just above the front door, into the ceiling, out through the exterior wall, up the wall into the loft, across the loft, down into the airing cupboard, through the wall into the bathroom, through some pipe boxing to the rising water main.
All so I didn’t have to pull up the fitted carpets and floor boards.
This is what I believe muddies the waters between GSR's and sparks!
This is an ongoing issue between the trades and you can spend the whole day arguing with a plumber who is trying to tell you where to place your main bond! At the end of the day electricians have their regs and plumbers have their regs,
I was taught that you bond inside and if plums don't like it they can waste their day arguing on the phone with gas safe or niceic or whoever they choose
I had this argument concerning a second-floor gas pipe ran from an external meter up on the outside wall through the wall to isolator valve to combi boiler it was bonded after the isolating valve. expected the 10mm earth to run from the flat outside to the meter showed him regs book still wouldn't have it. As far as I was concerned it was installed to regs left him to it to explain to the builder why 8 earth wires had to be run down the external walls.
Main bonding - Green and yellow conductors that connect metal pipes (gas, water or oil) from inside a building to the main earthing terminal of the electrical installation. Main bonding connections may also be made outside the building, for example where a semi-enclosed gas meter box is installed outside and it is not possible to install a bond to the gas installation pipework indoors.
you better tell all the sparks in uk their are doing it wrong gas out side meter .
If you want to comply with BS 7671 then that states that it must be after entry to the premises, or words to that effect.
If you put it outside then it is a deviation that must be noted.
Then, if you bond outside, you must defer to gas regulations as to how you bring the cable into the premises, if, you do this within the meter enclosure, and that is the law of the land, not some industry recommendation such as BS 7671.
So, where is that from?
Well as I said originally the question I was pondering was what did it mean ...at the point of entry into the building...? Is the point of entry when it gets inside or the point of entry where it starts to go inside. So if a person is at the front door they are ...at the point of entry... inside the front door they have entered the building so entry has been achieved. Ok maybe I think too much. You see in the olden days there were no gas meters outside in domestic. So it was all fairly clear, and quite common to bond water and gas under the floor boards. Perhaps not the brightest idea in retrospect but accepted practice. It was just that gas safe man has the idea bonding has to be on the meter outlet pipe and viewable I presume. But then what is he doing judging on such a matter???
It’s so obvious that you copied and pasted Buzz - or did you find you glasses!
Regs say point of entry, nothing about inside or out.
The thing is quite simple.
If you always place your main bond on the inside of the property it will always be acceptable and compliant with bs7671.
If you decide to place your main bond outside the property there are times that will not be acceptable.
On that basis just bond inside and you can't go wrong. What is to debate?
Just bond it! It really makes no difference whether inside or out as long as an appropriate clamp and common sense are used.
It makes a difference where the bond is if you are trying to do an R2 test and you have to go outside the property to get to the connection. Installing the cable outside is also more work for the electrician and additional cost for extra cable. Therefore your claim that it doesn't matter whether it's bonded inside or outside doesn't hold water. Inside is easier and cheaper.
How b l o o d y stupid ...
You would have hoped that the gas regs simply referred to a regulation in BS 7671
Then there would be confusion, no ambiguity,
Ah, utopia
Not to mention the gas regs state that the gas pipe must always be bonded, if you test and it's not extraneous then there's no need to bond it at all, same goes for plastic water incomers.
I bet the gas guys would have a fit if you explained that to them though.
Anyway, that document posted by Murdoch only says they need to notify in writing, doesn't say they should refuse to proceed.
1. It's not an R2 test is it?
2. Unless my regs book is different from others it actually states-
544.1.2 - The main equipotential bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises, Where there is an insulating section or insert at that point, or there is a meter, the connection shall be made to the consumer's hard metal pipework and before any branch pipework. Where practicable the connection shall be made within 600mm of the meter outlet or at the union point of entry to the building if the meter is external"
3. It doesn't as far as I can see mention, 'more work for the electrician' or 'additional cost of extra cable' or I don't think 'inside is easier and cheaper'
I rest my case.
if you put the bonding under the floor boards to the copper pipes there is more likely that the bonding clips might rust with moisture .
I disagree there Buzz. There are plenty of external meter cabinets I see with missing covers and are much more likely to 'feel' the elements. Also if you use the correct grade of 951 clamp there should be less of an issue still.
I have had this issue once where routing the 10mm would have been a pita to take it externally. I terminated it just inside at the point of entry into the building itself. Left a big label saying 'plumbers are t00ssers" to grab their attention and then another underneath saying that the bonding was upto scratch with BS7671 2015 and where the pipe was bonded.
Is it not the case that even if the incoming gas is fed in plastic, that the actual internal gas pipework being metallic does require bonding still. I seem to recall reading that in the regs approx 4 years or so ago. If I recall correctly it applied specifically to gas but not to all metallic water pipework (even when the incoming water was plastic too).
The requirement is to bond extraneous conductive-parts.
Plastic is non-conductive, so doesn’t require bonding.
Metallic pipework inside the building is not extraneous, so also doesn’t require bonding.
When you look up the definition of extraneous conductive-part, it says something about not being a part of the electrical installation which may introduce a potential (might be introduce a difference in potential).
Determination of whether the pipework introduces a potential (or a difference in potential) would indicate whether it requires bonding.
I’m pretty certain this has been covered a number of times.
Use an IR tester to determine whether there is any continuity between the installation earth and the pipework and use a low ohm meter to determine whether any continuity found is reliable.
Below 0.05 ohms is considered reliably connected and doesn’t require bonding.
Anything between 0.05 ohms and 23 kohms would be considered as being in contact with earth, though there are different opinions regarding the higher end as to whether it would require bonding.
22k ohms, 1667 ohms or 667 ohms, all dependant on the resistance of an average human body (1 kohm) and the 50v considered as being safe.
Shirley the reason to bond as per reg 544.1.2 is that if some plumbing bod comes at a later date and re-routes the gas pipe (metal), the gas pipe is more likely to remain bonded, than if original pipe was bonded under the floorboards half a mile away. And don't say its down to the new plumber to make sure, 'cos it ruins my argument. So the nearer to where the gas pipe becomes metal after the meter, the better (if its extraneous of course).
I rest my case.
Regarding points 1,2 and 3. (Which you have separated and quoted simultaneously so I will answer all 3 with a single reply .
1.
I never said it was an R2 test did i?
R2 was mentioned as it is going to be more practical and convenient for the verification of the main bond in the future,and when installing equipment you should do so with due consideration for the cost,maintenance and convenience of the client. Therefore bond it inside and yes it definitely does make a difference if it's in or out. Installation work is primarily for safety and convenience and you should bear this in mind at all times.
1.
What if the gas pipe is inaccessible for most part inside the building but readily accessible at point of entry outside but within the gas meter enclosure? I have come across this situation many times. For me the obvious and most convenient answer, in these situations, is to bond at external point of entry.
then you bond to the pipe work out side has long you can get to it.
1.
Really?:rolleyes::rolleyes:
You would just use your common sense as you would in any other scenario.
The instances where it is easier to bond outside are the exception to the rule
With the vast majority of new builds with meter boxes or enclosures (circa 1970's) installed on the outside, the only practicable way is in the box itself. Is that inside or outside?
If you find it hard to accept that it's easier,cheaper and more convenient to bond inside then you haven't ho
The gas pipe that is outside in the meter box has got to enter the property at some point so the most practical position to bond the pipe would be on the inside of the property 'at the point of entry'. How the hell is drilling a hole and going outside to install the clamp 'the only practicable way'??? How is a job that takes longer preferable to a quicker method? (Unless you are on dayrate)
Like a lot of properties in such situ's the gas pipe is not always accessible on t'other side of the wall where the meter is mounted. Can't really see how either way would take any longer or would be quicker.
Inside is nearer to the consumer unit and you can't see how it makes any difference to use less cable instead of using more cable? Seriously???
Reply to Bonding to gas and 544.1.2 in the UK Electrical Forum area at ElectriciansForums.net
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
We had our gas disconnected last week and the meter removed. We need to start removing the redundant gas pipes in inside the property. There is...
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...