E
EWebster
Hi all,
A customer doesn't want a new consumer unit, but wants work doing to an existing lighting and existing ring circuit.
I believe I'm correct in thinking that if I do work on these older circuits, I must then RCD protect them. Is it better to fit an RCD to the incoming mains, before the fuse box, or individually RCD protect each of the two circuits?
Many thanks
EW
if you are goin to rcd the whole board you will need to also fit a main switch before the rcd. I would fit rcbo's on the individual circuits. It will stop nuisance tripping of the whole board.
Sounds like a plan. I'm assuming I can get push in RCBOs to replace the fuses?
Regards
You cant get RCBO's to replace push in's.........probably best fit a small enclosure alongside the DB with a couple of RCD's in .
Why do you say that he needs to fit a main switch before the rcd ?
As an rcd should not be the main mean of isolation for the installation.
I spoke to NICEIC yesterday, and he cited the regs, saying that there is provision in the regs for using an RCD as a main switch.
Seems to be a bit of confusion around this area. :confused:
yes you may have an rcd as a main switch see the regs for tt systems shud clarify the situation cheers ceri
Single main RCD or multiple
EWebster,
cegsdj,