willij

On the first pic, the left hand SWA comes in and is wire to the supply side of the 3 phase breaker, it feeds another distribution board. Is it legal?

On the second pic, it's a 3 phase board wired as a single phase. There is nothing to say that it's single phase, I only found out when the cover was taken off. Is it legal?

Regards...
 

Attachments

  • IMG_0879.jpg
    IMG_0879.jpg
    121.8 KB · Views: 226
  • IMG_0322.jpg
    IMG_0322.jpg
    215.9 KB · Views: 260
  • Like
Reactions: 1 person
I take it these are for control or very light loads? What do you think's wrong with them?
I would put a label on to identify what they are. End of problem.
 
Last edited by a moderator:
What size cable is going from DB1 to DB2? What is the size of MCB protecting this cable? This may be a problem...
 
Pics 1 whats the protective device feeding that DB and pic 2 not wrong as the links are sized as per the supply. Would of been better to use a conversion kit though IMO
 
I would be straight off to the supply end of the DB to check breaker size against the small cable cos there's a big difference in cable size there. Could be a serious problems as the little cable may not have an effective ADS
 
It looks like the SWA at the bottom left of the DB is supplied straight from the main switch without any OPD !


Is that what you are on about Will ?
 
Need we caps on the live stumps.lol.

Say you have 6 x 3 phase switch places and the main switch is at the bottom, can you add to the bus bars for additional ways???????? If you know what i mean..

Say make 6 way , into 8 way
 
On the first pic, the left hand SWA comes in and is wire to the supply side of the 3 phase breaker, it feeds another distribution board. Is it legal?

On the second pic, it's a 3 phase board wired as a single phase. There is nothing to say that it's single phase, I only found out when the cover was taken off. Is it legal?

Regards...

Pic one could be an issue....
Or it could be back fused if the cable is less than 3m and goes to another OCPD.

Pic 2 looks ok, aslong as the links are the same size as the supply.
Prefer to see a conversion kit though...
I'd relabel the db into single phase numbers.
 
  • Like
Reactions: 1 person
On the first pic, the left hand SWA comes in and is wire to the supply side of the 3 phase breaker, it feeds another distribution board. Is it legal?

On the second pic, it's a 3 phase board wired as a single phase. There is nothing to say that it's single phase, I only found out when the cover was taken off. Is it legal?

Regards...

In pic 1 I think he is saying that the small cable that he has his hand on ostensibly feeding another db, if you look closely you cam see the larger cables that feed this db behind them. What size is the fuse that feeds this arrangement? If the fuse is too bog for the second cable (the one that comes of this board) the cable needs to be increased or the fuse downgraded. Nothing wrong with pic 2 just label it up as single phase.

Sent from my GT-I9100 using Tapatalk
 
In pic 1 I think he is saying that the small cable that he has his hand on ostensibly feeding another db, if you look closely you cam see the larger cables that feed this db behind them. What size is the fuse that feeds this arrangement? If the fuse is too bog for the second cable (the one that comes of this board) the cable needs to be increased or the fuse downgraded. Nothing wrong with pic 2 just label it up as single phase.

Sent from my GT-I9100 using Tapatalk

A smaller cable can be taken from there to feed a small unit. Aslong as it is back fused.
It's common.
 
The cable in pic one with his hand on is obviously not the feed to the second board because if it were the neutral and earth conductors in the single phase board would actually be L2 &L3 the way it's connected!!!! I'd say the first pic defiantly requires fixing as there is no overcurrent protection for that smaller cable, a sub feed from that DB should either have come from a spare way or if no room taken through an enclosure and MCB next to that point.
The second pic is fine, You can actually buy linking kits to do this properly (mini bus bar that sits across the main switch) but as this is the old style it may not have been available at the time.
 
The cable in pic one with his hand on is obviously not the feed to the second board because if it were the neutral and earth conductors in the single phase board would actually be L2 &L3 the way it's connected!!!! I'd say the first pic defiantly requires fixing as there is no overcurrent protection for that smaller cable, a sub feed from that DB should either have come from a spare way or if no room taken through an enclosure and MCB next to that point.
The second pic is fine, You can actually buy linking kits to do this properly (mini bus bar that sits across the main switch) but as this is the old style it may not have been available at the time.

Could feed a 20amp tpn fussed isolator??
I think the spark testing should be able to identify this and if its acceptable.
 
Drawing.JPGFirstly, thank you very much for your responses. I was allowed to go home early on Friday afternoon, that's why there has been no reply from me.
I’ve attached a drawing of the supply to the DB in Pic 2
The DBs in the pics are not connected, they are in different locations, my concerns are for both of them. I hope I have been able to explain things below.

Pic1: The one with the finger.
The smaller 3 phase cables on the supply side lead to an isolator, which in turn leads to a 32A socket (3P+E). There is no breaker to protect it except for the one that protects that DB itself, i.e. the DB is supplied from 100A breaker.

Pic 2: See attached drawing.
This being wired as a Single Phase board… the red cable is actually coming from the load side of the main supply switch to the building (250A switch). The only way to isolate the board is to switch the power off to the whole building. The NS100N switch in the attached drawing is wired as shown… nothing connected to the load side.

Thank you again...
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
DBs, is this legal?
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
23

Thread Tags

Tags Tags
legal

Advert

Thread statistics

Created
willij,
Last reply from
sparkenter,
Replies
23
Views
3,512

Advert