got a query, just questioning my judgemet

been o look at a job were a spark has done a disappearing act and work needs finishing the scenario-

total rewire, new3 phase mains incoming and gas etc

5 storey building
x4 new flats all new installs

by the entrance ground floor x4 submains each has 100a switch fuse cutouts for each flat and a landlords c/u. all fed via 25mm 3 core SWA from DNO 100a cutout in the basement.

my thinking is they should have switch fuses in the basement as its 20+ metres from DNO cutout to the switch fuses?

also the landlords supply has no switch fuse at all, just straight from DNO isolator.

the 2 mini boards are for pump for 2 of the flats

pic
 

Attachments

  • drapery board.jpg
    drapery board.jpg
    160.1 KB · Views: 137
So there unsheathed cables from the output of the isolators?
 
Looks shocking.

Get yourself some trunking and grommet strip
 
  • Like
Reactions: 1 person
Agree mate but didn't want to sound rude but you did it for me
 
One mor observation what about sleeveing on the cpc
 
this is how I have found it, the swa sheath wasn't even earthed, which I have done.

not sure how to get around the unsheathed cores
 
I don't think its the fellas work if I'm right, but yea was thinking that, bit of sleeving.

Anyway those tails from the armoured will get snagged too.

I can't look at that pic any longer.
 
the tails from aroumered run through a bush, so go through metal trunking without harm but, I really don't know why he has done like this
 
im carrying out an EICR as agreed, as they need building regs approval asap, they did want me to sign off as mine!! hhhmm don't think so
 
  • Like
Reactions: 1 person
the tails from aroumered run through a bush, so go through metal trunking without harm but, I really don't know why he has done like this

They should be in an enclosure.
 
Thats right or M/C switch fuses bushed directly into the metal trunking eliminating the need for non sheathed armored cable cores
 
I would love to see whats hiding to the left of the picture
 
it does need switch fuses at this location doesn't really?
as from here its 20+ metres to the ground floor switch fuse isolators he has installed
 
Alright I'll be a brave boy bloody awful rip it out and start again, complete crap
 
Hi,

I don't know where to start , there is so much wrong with it. As Pete says rip it out, start again and do it right. Trying to put right what is already there will take longer than re-doing the job.

Regards.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
flat submains and landlords suuply
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
pbarrett,
Last reply from
7029 dave,
Replies
43
Views
5,924

Advert