sparksburnout

-
Esteemed
Reaction score
1,766
I have a domestic premises (it was once a shop) that has a three phase supply, although only one is being used now. I am using a di-log 9083P tester, and when doing a Ze test am getting 23KA as the reading for PSC, with 0.01 ohms as the loop resistance. I am getting a Ze of 0.35 ohms and a PFC of 565A. The values for PSC and L-N loop impedance seem unbelievably low to me? I am not sure where the local transformer is but it is not next door, I think it is about 400yds away. System is TNS. I have looked at the thread in the I&T forum, and used the method of inserting an impedance in the earth lead of the tester, but I am still getting the same readings, which as far as I can see you would, as it is for low Ze not low PSC. I have used the tester on about 3 other installations, and it is giving expected results. Could it be possible that these values are correct? In which case the main switch and breakers are well underrated!!
 
just check your readings again will you on Zpn....caus 23KA ffs....
I know! I just tried it again over the road at my mates house, and it's giving very similar readings now - the previous ones I mentioned were Zs. This meter is quite new, I suppose it could be faulty, or is it that these meters are just not capable of working properly at low Ze's? It is still giving a P-N loop res of 0.01 ohm that can't be right even if the transformer was next door???
 
I know! I just tried it again over the road at my mates house, and it's giving very similar readings now - the previous ones I mentioned were Zs. This meter is quite new, I suppose it could be faulty, or is it that these meters are just not capable of working properly at low Ze's? It is still giving a P-N loop res of 0.01 ohm that can't be right even if the transformer was next door???

Hi if I leave my megger in the van over night when it's cold I get strange pfc and loop readings I leave it inside in the warm for a hour works fine it has been calibrated a few times now with out any problems,had me scratching my head at first
 
I know! I just tried it again over the road at my mates house, and it's giving very similar readings now - the previous ones I mentioned were Zs. This meter is quite new, I suppose it could be faulty, or is it that these meters are just not capable of working properly at low Ze's? It is still giving a P-N loop res of 0.01 ohm that can't be right even if the transformer was next door???
it can be 0.01, thats what it is at the factory i work at
 
i've hundreds of photos like that from around the country, when we go to caravan sites i stop and take a pic whenever i see one. our lass says im a sad b*****d.
 
i also collect spades and have a decent colletion, my best been a 1930's cast steel digging spade double braced on ash shaft with a box "D" handle.

- - - Updated - - -

love watching old fred dibnah episodes on sky.
 
i also collect spades and have a decent colletion, my best been a 1930's cast steel digging spade double braced on ash shaft with a box "D" handle.

- - - Updated - - -

love watching old fred dibnah episodes on sky.

Yes .... he was a grand bloke.

I must say I admire blokes who can call a spade a spade.

Tidyboiler tells me her Dad ( a tough little Pikey bloke) always called a spade a spade and often to his face.

I have a collection of woodworking tools that were made and used by my Grandfather in a very impressive tool chest that he made himself.

I think to a collector they will be worth some money.
 
it was fred dibnah who got me into traction engine rallies (not personally mind) cant wait for pickering's rally in august.

I used to get around a lot but haven't been able to for the past couple of years cos I've not been well.

I always wanted a good camera outfit and after about 30 years finally got it - all packed in a big fluck off rucksack that I can't carry .......
 
well i do hope your health starts to improve:20:

Thank you.

I appreciate that, the past months since October have not been much fun, but could be worse. I think I'm picking up a bit now since Friday when Tidyboiler almost literally dragged the GP by his balls from his full surgery direct to my bedside!

I had his full attention from then on.
 
I used to get around a lot but haven't been able to for the past couple of years cos I've not been well.

I always wanted a good camera outfit and after about 30 years finally got it - all packed in a big fluck off rucksack that I can't carry .......

go on then. keeping us in suspenders, what camera?
 
Meanwhile back at the OP.
Might sound silly but how are you off for charge in the battery pack? Many testers start to give really daft readings if they're low.
I also think you may need to check your reading as it does not work out to 23Ka
 
Furthermore, a Ze of 0.1 ohms at the distance you quote from the transformer is unlikely in my experience. I once did a rewire less than 50 metres from one and the reading I got was 0.47, considering how streets are wired this isn't beyond the realms of possibility but I checked it with different testers both very recently calibrated and they agreed.
I'd definitely be checking those batteries mate.
 
Canon 30D

Old(ish) but does the job - a bit like you Tel.

Bag full of assorted lenses -Canon & Sigma, Sigma flashgun, Manfroto tripod and a monopod (one legged tripod) bits & bobs and I can't lift the bloody thing.

nice. i have the 10D. even older.does everything i need, though. only gripe i have is the size of the LCD screen 1.8".
 

Reply to Problem with PSSC on three phase supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
320
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Probably more of a maths problem than anything else / managing to confuse myself. I have been asked to look at energy consumption of some...
Replies
7
Views
567
Hi everyone, each leakage question here. I am needing to run some LED screens, professional type, not TVs. These are 500mm x 500mm panels and...
Replies
11
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top