Search the forum,

Discuss Can you take 2 phases to a consumer unit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Gigsy

-
Reaction score
46
Hi,

I am training to become and electrician, I have passed my C&G level 2 exams. I am working as an electrical improver.



I came across a consumer unit today, which has two main switches and two phases L2 and L3 supplying it.



Does this board comply with regs?



Can you take 2 phases to a consumer unit?

31649325_1836209529831911_725720731379302400_n.jpg
 
Ok well I am thinking why are there three neutrals on the first block on the right does this mean the neutral will be switched off with the first main switch, it is a bit hard to follow where the three neutrals go.
 
T
An enclosure and assembly absolutely can be rated for 400V or not as the case may be.

There is nothing on the metal box which identifies it as being rated for anything, The switches are rated for 400v. But they are only subject to 230v each?
It is a normal domestic consumer unit?

switch.jpg
 
T
An enclosure and assembly absolutely can be rated for 400V or not as the case may be.

There is nothing on the metal box which identifies it as being rated for anything, The switches are rated for 400v. But they are only subject to 230v each?
It is a normal domestic consumer unit?
 
Ok well I am thinking why are there three neutrals on the first block on the right does this mean the neutral will be switched off with the first main switch, it is a bit hard to follow where the three neutrals go.
Incoming neutral goes to 1st neutral bar.
Then linked from there to each switch
 
T


There is nothing on the metal box which identifies it as being rated for anything, The switches are rated for 400v. But they are only subject to 230v each?
It is a normal domestic consumer unit?

That’s unusual, those contactum boards always used to have a label on the lid identifying the BS-EN standard they are built to, this standard will give the voltage and PSCC they are rated to. Maybe the sticker has fallen off?
 
That’s unusual, those contactum boards always used to have a label on the lid identifying the BS-EN standard they are built to, this standard will give the voltage and PSCC they are rated to. Maybe the sticker has fallen off?

I will take a look on the lid tomorrow, thank you.
 
That’s unusual, those contactum boards always used to have a label on the lid identifying the BS-EN standard they are built to, this standard will give the voltage and PSCC they are rated to. Maybe the sticker has fallen off?

I don't really understand this statement.

The metal box is just a metal box. The accessories inside the box ie. the switch, the RCD's and the MCB's are all marked with BS-EN numbers and breaking capacity numbers. Each accessory is only at a potential difference of 230v. I can do a PFC and PSCC test on the installation, but I know for a fact the tests will not exceed 6kA. Why do the accessories need to be rated at 25kA?
 
Last edited:
I don't really understand this statement.

The metal box is just a metal box. The accessories inside the box ie. the switch, the RCD's and the MCB's are all marked with BS-EN numbers and breaking capacity numbers. Each accessory is only at a potential difference of 230v. I can do a PFC and PSCC test on the installation, but I know for a fact the tests will not exceed 6kA. Why do the accessories need to be rated at 25kA?

Not strictly true,as someone has had to assess,test,approve and certify that "box".

A test of this,is how many DB's with the equipment listed,have you seen,with a home made enclosure?
 
I thought if you were going to use more than one phase, you used three to balance the load? So why would you use a domestic CU designed for a typical single phase domestic property, when you could use a properly designed three phase board, intended for that use?

The 3rd phase (L1) goes to a consumer unit downstairs. I think they have balanced the load.
 
Not strictly true,as someone has had to assess,test,approve and certify that "box".

A test of this,is how many DB's with the equipment listed,have you seen,with a home made enclosure?

It is not a home made enclosure, It is made by contactum.
The box has a 400v sticker on it, so anybody who wishes to service it knows the potential voltage.
 
Hi,

I am training to become and electrician, I have passed my C&G level 2 exams. I am working as an electrical improver.



I came across a consumer unit today, which has two main switches and two phases L2 and L3 supplying it.
I can see where you are coming from Gigsy, might seem a daft question but have you actually confirmed that the voltage between L2 and L3 is 4oo volts, I only ask because it seems an odd installation to me, probably barking up the wrong tree, but I thought I would ask just to be sure.



Does this board comply with regs?



Can you take 2 phases to a consumer unit?

View attachment 42245
 
not sure about regs. but I'd not be comfortable with it.(even if the wiring was not a rat's nest).
 
Hi,

I am training to become and electrician, I have passed my C&G level 2 exams. I am working as an electrical improver.



I came across a consumer unit today, which has two main switches and two phases L2 and L3 supplying it.
I can see where you are coming from Gigsy, might seem a daft question but have you actually confirmed that the voltage between L2 and L3 is 4oo volts, I only ask because it seems an odd installation to me, probably barking up the wrong tree, but I thought I would ask just to be sure.



Does this board comply with regs?



Can you take 2 phases to a consumer unit?

View attachment 42245
 
Are you SO sure?
He seems to be defending its use rather than learning the reasons its not really suitable.

No mate, I'm not sure. Just quoted what the OP stated in his first post. Lest ask...
I came across a consumer unit today


@Gigsy . Did you wire up this CU or do any changes to it?
 
Don't know if my last post went anywhere Gigsy, may seem a daft question, and I'm only asking because I'm not sure what I'm looking at, but have you canfirmedthat there are 2 phases present, by testing the Voltage between L2 and L3
 
The 3rd phase (L1) goes to a consumer unit downstairs. I think they have balanced the load.

Long time since I did any 3 phase stuff, but that doesn't appear to be a very good design. Either of those two DB's could be altered over time, and without in depth knowledge of the installation, one could be significantly altered in preference to the other. Unlikely to happen in a single dedicated 3P DB, IMO.
 
It is not a home made enclosure, It is made by contactum.
The box has a 400v sticker on it, so anybody who wishes to service it knows the potential voltage.

Hi gigsy,
It's not a home made enclosure, but someone has adapted it in such a way as it no longer resembles or performs as it was intended. Therefore it's a home made adaption to fit a second phase that it was not intended for.

P.S. What is an electrical improver?
 
Hi gigsy,
It's not a home made enclosure, but someone has adapted it in such a way as it no longer resembles or performs as it was intended. Therefore it's a home made adaption to fit a second phase that it was not intended for.

P.S. What is an electrical improver?
It used to be in my time, someone who had done an apprenticeship and would normally spend the next 6 months as an Improver, that was what I did, mind you that was early 1960s. Don't know what it is these days what with apprenticeships the way they are structured.
 
Hi Gigsy, been keeping busy I see !
These boards are intended by manufacturers to be used for single phase. For more than one phase a 3 phase board should be used, in my humble opinion. I would drop an email to manufacturer's tech dept for their view.

Very good advise, thank you :)
 
Are you SO sure?

He seems to be defending its use rather than learning the reasons its not really suitable.

I would have said that this "box" needs a 3P isolator, in it, or at the very least adjacent to it.

I want to know if the board breaches any regulations. I have passed C&G level 2 regs exam. As far as I can see, no regulations have been breached here. I need to know so I can advise the owner of the building, if there is a breach of a regulation. I am not going to tell him this board needs changing until I know for sure it does. The work required to put it right (if anything is in breach of any regs) would be over £1000 in my opinion.

Is there is regulation which state a 3 phase isolator needs to be adjacent to it, or did you just make that up? If so can you give me the regulation number please?
 
No mate, I'm not sure. Just quoted what the OP stated in his first post. Lest ask...



@Gigsy . Did you wire up this CU or do any changes to it?

We have removed a circuit from this board.
Don't know if my last post went anywhere Gigsy, may seem a daft question, and I'm only asking because I'm not sure what I'm looking at, but have you canfirmedthat there are 2 phases present, by testing the Voltage between L2 and L3

Yes 400v between L2 and L3
 
Long time since I did any 3 phase stuff, but that doesn't appear to be a very good design. Either of those two DB's could be altered over time, and without in depth knowledge of the installation, one could be significantly altered in preference to the other. Unlikely to happen in a single dedicated 3P DB, IMO.

Agreed a 3 phase board would have been a better choice.
 
Anyone else notice the screws arnt done up (top left and right) someone could lift it up and pull it off the wall :D

The board was not powered at the time the photo was taken. We took the bottom screw out, the top screws are meant to be loose, you hang the board on the two top screws, then secure it with the bottom screw.
 
It's Single Phase Consumers Unit and should be treated as such, not designed for more than a single phase supply, any difference doesnt comply with BS7671 In my opinion, don't really understand what all the debate is about.
 

Reply to Can you take 2 phases to a consumer unit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
499
Can you feed a consumer unit from another consumer unit, It would be supplied by a non RDC protected MCB. Is this allowed as I have always seen...
Replies
3
Views
2K
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
911
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
807

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock